As title, just clocked this on a job I am on, all conductors correctly sleaved,

Has anyone saw this before?

I have always used 3core&e
 
All 230volt circuits require a cpc, even if it isn't connected to a piece of equipment that needs earthing, so my answer is no its not wired correctly and anyway a flex shouldn't be used as fixed wiring in my opinion.
 
would a circuit that is soley dedicated to smoke alarms require connected earths at each point even though they wouldnt be connected

Yes - all points must be earthed and these connected back to the consumer unit or D.B., even it the point has a class fitting on it.
 
Whether the load (alarm/light/socket) needs an earth or not is irrelevant. As has been stated the cable itself needs an earth to help detect faults if it is damaged. I believe this is why in T&E the cpc is not sleeved: so that a damaged line or neutral has more chance of touching it and tripping the protective device. Otherwise it would need the insulation of the line AND earth to be damaged to make a connection to the CIRCUIT protective conductor.
 
I have actually just had to purchase 100metres of 3core & earth 1mm for a little commercial job. £42 incl vat......so I think it goes down to lazyness oppose to cost, as I am sure flex is a bit more expensive than that......correct me if I am wrong
 
All 230volt circuits require a cpc, even if it isn't connected to a piece of equipment that needs earthing, so my answer is no its not wired correctly and anyway a flex shouldn't be used as fixed wiring in my opinion.

Absolutely nothing wrong with it when used appropriately. Not saying this is appropriate though!
 

Reply to Interlink smokes wired in 3core flex in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
381
Any issues with wiring lighting in 4core flex rather than 3core and earth? Approximately 50 LED panels to wire all fitting into a suspended...
Replies
19
Views
1K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
I have a spare 2.5mm 3 core flex cable. Can I use it for an outdoor light? It will be connected a junction box that's already supplying...
Replies
2
Views
1K
Hi, The wire of my dehumdifier is broken (Meaco 20L Low Energy). The wire was being pulled over a period of time, which seems to have lead to a...
Replies
3
Views
240

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top