Hello - I hope someone is able to help. I have three light switches (2 x 2-way, one with a dimmer, and an intermediate switch). I seem to have trouble with my intermediate switch. Both the 2-way switches/dimmer work as expected. But if I switch the intermediate, the light goes on and neither of the 2-way switches switches the light off. I've had a check of the intermediate wiring and it appears to be fine. So I'm quite puzzled. I thought the behaviour description might enable someone to explain what is happening. Thanks in advance for any help!
 
TL;DR
Strange intermediate switch behaviour
What is it you have done replaced the intermediate switch?
 
Post photos of the connections at all three switches.
 
This is the 3 switches. I've posted 2 of the second dimmer switch. I'm just really puzzled that can get the behaviour from the intermediate switch. BTW - The 3, intermediate pic, the top two wires are black (but has a brown sleeve). I tried swapping the two brown wires at the bottom incase this would make a difference (thought I didn't think it would) but same. Thanks again....
 
To clarify why the behaviour is as it was...

When an intermediate switch is in the up position, L1 and L2 pass straight through from one 2-way to the other, so the switch is transparent. In the down position it crosses over L1 and L2, so that if the two 2-ways match in position it unmatches them, and vice versa. For the 2-ways to function, L1 and L2 'in' must pass through to L1 and L2 'out' either straight or crossed at all times.

With your mis-wired intermediate, in one position the condition was still satisfied that the 'ins' passed through to the 'outs' so the 2-ways functioned normally. If L1 and L2 'in' were on the same side of the switch, that would have been the crossed position. But in the alternative position, the switch spuriously looped each L1 back to the L2 from the same 2-way. (By interchanging the two browns you would have exchanged which intermediate position caused the loop-back)

One of two things would then happen. With 'conventional' 2-way, the older configuration where the permanent live goes to the common of one 2-way and the switched live is taken from the other, the circuit would be broken as there would no longer be any continuity between the two 2-ways. Thus the light would be off regardless of the 2-way positions. OTOH your wiring is 'conversion' 2-way where PL and SL are connected to L1 and L2 at one of the 2-way switches. In this case because the intermediate was looping L1 back to L2, it completed a circuit from PL to SL forcing the light on regardless of the 2-ways.

Therefore, your clearly-worded description:
Both the 2-way switches/dimmer work as expected. But if I switch the intermediate, the light goes on and neither of the 2-way switches switches the light off.

completely localised the problem to within the intermediate or its connections. Only two possibilities then existed: the switch had an internal short-circuit that only occurred in one position (e.g. because one of its two changeover contacts was operating but the other was jammed) or the wiring was incorrect.
 
To clarify why the behaviour is as it was...

When an intermediate switch is in the up position, L1 and L2 pass straight through from one 2-way to the other, so the switch is transparent. In the down position it crosses over L1 and L2, so that if the two 2-ways match in position it unmatches them, and vice versa. For the 2-ways to function, L1 and L2 'in' must pass through to L1 and L2 'out' either straight or crossed at all times.

With your mis-wired intermediate, in one position the condition was still satisfied that the 'ins' passed through to the 'outs' so the 2-ways functioned normally. If L1 and L2 'in' were on the same side of the switch, that would have been the crossed position. But in the alternative position, the switch spuriously looped each L1 back to the L2 from the same 2-way. (By interchanging the two browns you would have exchanged which intermediate position caused the loop-back)

One of two things would then happen. With 'conventional' 2-way, the older configuration where the permanent live goes to the common of one 2-way and the switched live is taken from the other, the circuit would be broken as there would no longer be any continuity between the two 2-ways. Thus the light would be off regardless of the 2-way positions. OTOH your wiring is 'conversion' 2-way where PL and SL are connected to L1 and L2 at one of the 2-way switches. In this case because the intermediate was looping L1 back to L2, it completed a circuit from PL to SL forcing the light on regardless of the 2-ways.

Therefore, your clearly-worded description:


completely localised the problem to within the intermediate or its connections. Only two possibilities then existed: the switch had an internal short-circuit that only occurred in one position (e.g. because one of its two changeover contacts was operating but the other was jammed) or the wiring was incorrect.

Elementary my dear Lucien.
 
And a picture paints a thousand words....

the photo of the connections with the browns at top, at blacks in bottom, it was presumed that wiring was in 3c&e, one brown and one black from each cable.

From experience, the solution was evident.

Elementary my dear watson
 

Reply to Intermediate switch issue on three switch light in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
581
Hi all, currently doing a job at a house where there are 3 switches In the hallway to control the hall lights. All 1 gang switches, one at...
Replies
2
Views
571
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
716
Good afternoon, I wonder if someone could please give me some advice on a problem I am having with my bedroom lights. I have replaced the...
Replies
2
Views
1K
Hi, I am looking to convert a 2 way light into just control by single switch. I have searched and looked for similar questions here, and found a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock