Hi Guys,

I have just been in a house that is experiencing problems with a hall/landing light and the 5 (yes 5!!!) switches that control it.

So here's the layout:

There is a 3 gang dimmer on the ground floor with one gang for the light in question

3 intermediate switches on the landing (landing is horse shoe shaped and there is a switch outside each bedroom door)

1 gang 3 way switch outside the bathroom.

At face value it all looks like its wired correctly. There is a common, L1 and L2 at the dimmer, and the same at the 1 gang switch, and L1 L1 in L2 L2 out at all 3 intermediates.

I can turn the light on and off at each individual switch, but when i turn the light on at 1 switch and off at another the switches then don't work at all and i have to go back to the dimmer switch to turn the light on again.

Can anyone help me solve this problem so that any switch can be operated at any time to turn the light on and off.

Cheers
 
Re: Intermediate switch problem - Please Help!!

first thing is to check if it's not the dimmer.if the dimmer is turned right down, then the other switches will appear not to work as the lights are controlled by the dimmer. second is to see if you have the common in the 2 way switches linked with connectors in the intermediates if the L feed is not in the common terminal of 1 of the 2 way switches. if it's into L1 or L2, then you need 3 strappers.
 
Re: Intermediate switch problem - Please Help!!

second is to see if you have the common in the 2 way switches linked with connectors in the intermediates if the L feed is not in the common terminal of 1 of the 2 way switches. if it's into L1 or L2, then you need 3 strappers.

Cheers Tel,

I didn't see any connectors behind the intermediates, however i was getting 240v at each intermediate from one of the terminals.

I will check the dimmer and keep it turned up.

Keep you posted!!
 
is the dimmer turned right down? where does the L feed enter the switching system. if it's a loop in at light with L feed going int L1 of 1 of the switches, you need 3 core to the intermediates, with the 3rd core connected in each, straight through.
 
Re: Intermediate switch problem - Please Help!!

hmmm... my post appeared about 15 minutes after i'd posted it.thought it was dead, so, similar one follows when the forum wakes up.
 
is the dimmer turned right down? where does the L feed enter the switching system. if it's a loop in at light with L feed going int L1 of 1 of the switches, you need 3 core to the intermediates, with the 3rd core connected in each, straight through.

Thanks again Tel, I've posted this on 3 of the forums so apologies if you see it a few times. I'll go back and look for what you've said and hopefully rectify the problem.

Cheers for the help.
 
did it work ok before or as it always been like this, obviously if it as never worked then someone wired it wrong, if it used to work and now doesn't time to start testing
 
wrong!!!!! 1 way has common & L1. 2 way has common, L1, and L2. the 2 way switches the common from L1 to L2, hence 2 way.
 
Has it always been like that? Or is it a new fault?

I've had this before and it was a diy bodge job that had never worked.

Either way it's not complicated.
If you are having trouble visualising how the circuit should be wired, draw it out and compare it to what is there.

If it looks the same then it's a case of continuity test till you find the fault.
I'd be surprised if it took more than a few minutes TBH.
 
confusion between no. of ways and no. of terminals. standard of teaching is going down to socialist levels.
 
One strapper is open circuit between the two switches that have to be in particular positions for the light to work, or one of those switches has a faulty contact. Should find it in 2 minutes with a multimeter.

Edit: I read your description again and it's ambiguous - there are other possibilities according to exactly what you mean.
 
Last edited:

Reply to Intermediate switch problem - Please Help!!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
640
Hi all, currently doing a job at a house where there are 3 switches In the hallway to control the hall lights. All 1 gang switches, one at...
Replies
2
Views
547
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
871
I threw away an old knackered light switch and now need to replace it. It had 4 terminals (L1, L2, L3, L4) and is fed by two blue and two red...
Replies
8
Views
782
Suggestions / solutions please anyone? I have a 2 way switch, Hall and Landing, power being fed on Landing. When the switch is turned on, the...
Replies
2
Views
534

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock