Discuss intermittent RCD tripping..... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

J

J0N35Y

Morning.

Recently went to a job with what is a glorified shed, although fully insulated plastered, water tight etc, with a db installed within the unit. Small ring main and four down lights. The SWA supplying the 'shed' running back to the garage, on a 40a mcb protected by a 63a 30ma rcd main switch. Client had said that the rcd had kept tripping and tripped out the mcb for the shed at the same time. So to me narrows it down to the problem lying withing the shed. So all circuits tested within the shed as well as the SWA supply to the shed. No problems found at all. She did have a small heater plugged in the shed to help keep the damp.out, running for 3 hours a day (on the built in timer) on a low heat. Suggested the problem may be down to the heater. Heater unplugged.

Phone call two days later, had tripped again, no load on the shed this time. A little strange if you ask me.

Any ideas what to do next, what sort of direction to take?

Have since tested the whole board with the rcd on that supplies the garage sockets and alarm.
 
Agree with Marvo Ramp test at the RCD with no load connected , then also with the load connected and compare the readings ...
 
chicken and egg. is the RCD tripping first or is the MCB tripping and causing the RCD to let go.
 

Reply to intermittent RCD tripping..... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Curious one and hopefully some one of you could give me some advice. A customer has had a steeltech shed installed at their premises. A...
Replies
17
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
781
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
531
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock