- Reaction score
- 8,846
I'm doing testing ahead of a board change. It's a cramped Wylex rewirable installed by Spiderman himself. (I still haven't worked out why there seem to be 4 lives and 5 neutrals for lighting circuits, but that mystery will have to wait until the point of no return)
I eventually got the RFC lives and neutrals untangled and removed for an IR test. The cpc's are still connected unfortunately. L+N together to E at 250v is giving 8Mohms and slowly rising (reached 10 and still rising when I let go), but at 500v it's giving 0.5 Mohms.
Other than looking harder for connected equipment that I've missed is there anything this instantly suggests please?
I was suspecting outside lights on a FCU or something but can't see any.
(Zs is ok for all circuits. RFC continuity end to end is good too. Current main concern is this IR test result)
TIA
I eventually got the RFC lives and neutrals untangled and removed for an IR test. The cpc's are still connected unfortunately. L+N together to E at 250v is giving 8Mohms and slowly rising (reached 10 and still rising when I let go), but at 500v it's giving 0.5 Mohms.
Other than looking harder for connected equipment that I've missed is there anything this instantly suggests please?
I was suspecting outside lights on a FCU or something but can't see any.
(Zs is ok for all circuits. RFC continuity end to end is good too. Current main concern is this IR test result)
TIA