Discuss Intex Spa - No earth wire in power cable?!?! in the DIY Electrical Advice area at ElectriciansForums.net

STUART76

DIY
Reaction score
0
Hi

I have an intex inflatable spa and the moulded plug is hot to touch after running it for a few hours. I tried it in different sockets but it still gets hot so assume its the plug thats the issue. I cut the old plug off to attach a new one but there is only live and neutral wires. Is this right? Surely there should be an earth. There is an inline rcd (kp-g16b prcd) but is this enough to protect the spa? I'm hesitant to just wire a new plug on in case the moulded plug had some special arrangement.

Thanks

Stu
 
Have you looked at the instructions?
I suspect that it will say that it is double insulated and requires no earth.
 
Have you looked at the instructions?
I suspect that it will say that it is double insulated and requires no earth.

The instructions don't mention it, they just say it needs to be plugged into an earthed socket. However, instructions for a very similar design show that there are separate earth terminals that can be connected to household earth. You have to unscrew a plate on the back of the unit to get to them but why wouldnt the grounding go through the power cable to the wall socket. I guess I should be doing the grounding but I wonder how many people buy one of these things and just plug it in like i did expecting it to be earthed.
 
Is there a symbol on the rating plate which is a square within a larger square?
 

Reply to Intex Spa - No earth wire in power cable?!?! in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
1K
Hi.. Newby here.. I have a couple lights holders/bulbs on the end of a flex plugged into the mains 13Amp plug. I want to put an inline switch on...
Replies
3
Views
697
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
693

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock