Discuss IR connundrum in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Th
Hey Guys

I've got a bit of a head scratcher that I was hoping someone could help with.

I have a ring main feeding 7 points. When testing IR btw L&N I get 967Mohm but when testing N-E & L-E I get 455Mohm. I split the ring and tested as 2 radials and the results suddenly come back all clear at >1000Mohm L-N L-E and N-E??? When I reconnect the ring it's back down to 455Mohm??

I've checked all connections at the sockets and all good.

Any ideas??

Cheers
Mark
this is the kind of 'conundrum' I like to get on jobs, I.e the type you can just come back to think about when you are bored with nothing to do for an hour..455 Meg ..I want some of those conundrums in 2017
 
I t
Thanks for all the replies guys. I agree the results are good but I wasn't worried about them I was just curious as to why I was getting a lower reading when testing to earth. I was hoping to see them all around the same value.
otally understand why you wanted to know the actual reason as it is always helpful to know why things happen as opposed to just knowing that they happen,electrical theory is fascinating and the more you learn,the more you realise how little you know...hence why most avoid asking 'why'....
 
Hey Guys

I've got a bit of a head scratcher that I was hoping someone could help with.

I have a ring main feeding 7 points. When testing IR btw L&N I get 967Mohm but when testing N-E & L-E I get 455Mohm. I split the ring and tested as 2 radials and the results suddenly come back all clear at >1000Mohm L-N L-E and N-E??? When I reconnect the ring it's back down to 455Mohm??

I've checked all connections at the sockets and all good.

Any ideas??

Cheers
Mark

Disregarding, for the moment that with figures that high you shouldn't hesitate to move on. However it still can make sense.
The structure of T&E cable means there is about twice as much insulation between L-N as between LE or NE. So any leakage will be expected to be larger in the latter case. When you split the ring, assuming you broke it near the middle, each half L-E + N-E would be approximately doubled. Hence all 1000Mohm.
Wait till you get a damp installation 1000 times worse than you have there, and have to make a judgement..
 

Reply to IR connundrum in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
472
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
381
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
728
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
622
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
800

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock