Discuss IR test results. in the Australia area at ElectriciansForums.net

DNS1

-
Esteemed
Reaction score
771
Hi guys,

Tested my new kitchen circuit today, all results as expected for a new RFC except the IR between line and earth.

The resistance between line and neutral and neutral and earth is >1000 MOhms as expected, but between line and earth it's in the region of 3 MOhms.

After disconnecting parts of the RFC and re-checking, I've found that the insulation fault lies in one leg of the ring which runs above a ceiling and comes out in the new kitchen (this is the only re-used piece of cable from the previous installation).

I know it's not a major issue as it's "ok" according to the regs, but I'm wondering what's causing the problem.

Any suggestions for me?
 
if you've had plastering done, it could be damp. could also be a JB above ceiling or a problem in an existing socket.
 
I've removed a JB today in the offending section and crimped the ends instead, but no change to the readings.

As far as I can tell there are no other joints in the cable, it's just a straight run through a void above a downstairs ceiling.

No plastering done recently either...

Thanks for the help guys
 
Last edited:
can a new length of cable be pulled in...using the old as a draw wire?........if so then IR the length of new cable you plan to pull in first wont you....just to be sure as its a sod....doing the job twice that is..lol.....
 
Got to go with Glen on this one. OK it passes muster, but are you happy with it? I wouldn’t be. For the price of a few meters of 2.5 T&E and a bit of time I’d rip it out.

I also hate to say this but what about the rest of the installation? It could be you’ve just found the odd bit or cable that’s got a nick in it, but….

All right I can be a wet weekend at times.

Have a nice day

View attachment 10843
 

Reply to IR test results. in the Australia area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
622
Just your thinking on this… Doing Remedials on a EICR … the DB is a old Wylex with MCB”S/RCD Its a 10 way… rammed packed with cabling,,,the...
Replies
3
Views
1K
Evening all, Went round to a clients house and did some tests on an outdoor socket. At the junction (in an IP rated wiska box) between the cable...
Replies
6
Views
2K
Hi,guys went to do an EICR and when doing IR test I got L-E ON RFC like 0.02 MOHM and two lighting circuits L-E AND L-N the results were like 0,14...
Replies
6
Views
2K
Afternoon all. Bear with me on this one... Despite having been involved in the electrical industry for many years, I'm only just about to embark...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock