Discuss IR Test ? Weird issue N-E only in the UK Electrical Forum area at ElectriciansForums.net

Soulsurfer

-
Arms
Reaction score
143
Hey all, just doing some tests on a small extension and have a weird issue with IR on lighting circuit, all switches left open as nightmare to strip all lamps, fittings etc.. L&N to CPC not ramping up over 7-15V DC then resetting test !

L-N on 250V or 500V 31-32 Meg
L-E 32.6 Meg
N-E won't go ! Tried all obvious things to remove out of circuit plus new mains smoke detector etc.. but still no good, any ideas ?
Only fed at moment on a B MCB 6A no RCBO etc.. head scratching or feeding something hidden maybe or a fault ?
Thanks.
 
I still don't understand why you have left them open.
I figured in my early testing career that it would save frying any LED downlights or dimmer module etc.. as would take a good while to disconnect all fittings / lamps etc.. straight away. Tested at 100 & 250 V too to save any issues but none would ramp up test voltage to CPC
 
I still don't understand why you have left them open.
I figured in my early testing career that it would save frying any LED downlights or dimmer module etc.. as would take a good while to disconnect all fittings / lamps etc.. straight away. Tested at 100 & 250 V too to save any issues but none would ramp up test voltage to CPC
You should have the cpc connected to the earth bar.
Always done IR with every conductor out and in croc clips ? NIC assessor said was right way ? Thought would cause parallels if left in Earth bar ! Maybe I've made a fundamental boo boo
 

Reply to IR Test ? Weird issue N-E only in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
644
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
603
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
644
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock