Discuss IR testing in the UK Electrical Forum area at ElectriciansForums.net

Sb8389

-
Reaction score
25
Hi guys,
might make myself look stupid here
when wanting to carry out an IR test on a lighting circuit and you have sensitive equipment that you can't disconnect,if you do an IR test linking L-N to Earth is this basically the same as testing L-N.
the reason I'm asking is because I have an issue on a job where a customer is saying they are having an issue with there lights randomly tripping the MCB. I have already IR tested L-E and N-E and both came in at around 3.6meg, so I'm just curious if it's worth doing an L-N test and disconnect all loads

thanks for any replies
 
Testing LN-E just makes it so there's no imbalance between L and N so it shouldn't cause any damage, however if you have tripping I'd disconnect all loads and blast it with a trillion vaults
 
If it's randomly tripping what makes you think it ls a L-N IR issue?
Have you looked at the type of lights connected to the circuit and fully discussed the symptoms with the customer?
 
Hi guys,
might make myself look stupid here 
when wanting to carry out an IR test on a lighting circuit and you have sensitive equipment that you can't disconnect,if you do an IR test linking L-N to Earth is this basically the same as testing L-N.
the reason I'm asking is because I have an issue on a job where a customer is saying they are having an issue with there lights randomly tripping the MCB. I have already IR tested L-E and N-E and both came in at around 3.6meg, so I'm just curious if it's worth doing an L-N test and disconnect all loads

thanks for any replies

No, it is testing between the live conductors & earth.

Testing between line & Neutral is testing between the live conductors.
 
if it's the MCB that's tripping, then it's either

1. intermittent short circuit

2. " " overload

3. lamps blowing and taking the MCB out due to surge current.
 
Hi guys,
might make myself look stupid here 
when wanting to carry out an IR test on a lighting circuit and you have sensitive equipment that you can't disconnect,if you do an IR test linking L-N to Earth is this basically the same as testing L-N.
the reason I'm asking is because I have an issue on a job where a customer is saying they are having an issue with there lights randomly tripping the MCB. I have already IR tested L-E and N-E and both came in at around 3.6meg, so I'm just curious if it's worth doing an L-N test and disconnect all loads

thanks for any replies


What make you think it is an IR problem? if it was me I would check the current being drawn on the particular circuit in question, it could be that the circuit is working on the limit of the OCPD and trips randomly when someone say, swotches an extra light on, try it and see, you might be lucky.
 

Reply to IR testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
581
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
387
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
630
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
734
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
464

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock