Discuss IR Testing. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
25
On a two way lighting circuit ( wired in singles) how many times do you have to test to include the strappers?
Is it as simple as Switch One and then Switch two? (so two tests)
Or
Sw one, Sw two,Sw one again and the Sw two again.
If the latter is correct, that is four tests?
Or am I missing something?

Any help would be much appreciated.
Cheers
Gerry
 
I tend to turn lights on then isolate at cu then perform 1st test.
Then switch both switches so lights would be in on position again and then retest. So the answer would be twice.
 
On a two way lighting circuit ( wired in singles) how many times do you have to test to include the strappers?
Is it as simple as Switch One and then Switch two? (so two tests)
Or
Sw one, Sw two,Sw one again and the Sw two again.
If the latter is correct, that is four tests?
Or am I missing something?

Any help would be much appreciated.
Cheers
Gerry

You only have to switch one of your two-ways once to test the other strapper - that is 'per test'

In other words test L-E, throw switch, test L-E again. Test L-N, throw switch, test L-N again.

You don't have to throw switch during N-E test:)

Intermediates don't need to be switched, so a total of 5 tests
 
Last edited by a moderator:
No probs, Gerry.

As an additional thought, some wouldn't bother switching during the L-N test either (just L-E) - if the circuit was wired in T&E - as there wouldn't normally be a neutral in the vicinity of your strappers, but as you said it was wired in singles, then the strappers and neutral could be run together (e.g. in conduit), so best to throw switch and test again during L-N as well.

It's only one extra test, after all.:)
 

Reply to IR Testing. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

L
WIRING FOR WALL SMART SWITCH FOR CEILING FAN/LIGHT Just bought a smart wall switch for a ceiling fan/light currently connected to a single switch...
Replies
0
Views
735
littletwinn
L
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi all, Testing question for you. I'm currently testing an existing domestic installation. The wiring is about 20-25 years old. We have rewired...
Replies
7
Views
1K
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
328
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
472

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock