Discuss IR testing ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

B

BES

Hello all just reading Professional Electrician and noticed this on IR testing. Just wondered if anyone else was aware of this,came in with 17th in 2008. It slipped by me.:dunce2:

Live conductors and the protective conductor connected to the earthing arrangement. (Test 2)

Regulation 612.3.1 requires that the protective conductor has to be connected to Earth before the test is carried out. This requirement was introduced in the 17th Edition of BS 7671 in 2008. Prior to that time, it was acceptable to test between the live conductors and the protective conductor with the protective conductor disconnected from Earth. Often the cables were subsequently terminated without any further insulation resistance test being carried out. This is no longer acceptable.

However, insulation resistance testing between live conductors and the protective conductor, with the protective conductor disconnected from Earth, can be carried out during the installation process to ensure that the conductors have not been damaged during that process. It is good practice to carry out this test before part of the cable run is rendered inaccessible by, for example, partition walls being put into place.

Indeed, the sentence following Table 61 states that, ‘Table 61 shall be applied when verifying insulation resistance between non-earthed protective conductors and Earth.’

The lowest value obtained for Test 2 is recorded on the Schedule of Test Results as, ‘Live-E’.

Due to the vulnerability of electronic devices, which was mentioned above , it is acceptable to connect the live conductors together and measure between that point and the protective conductor when it is connected to the means of earthing, in accordance with Regulation 612.3.3.
 
Timboblefast
The point i was making is the part where it says you cant remove cpc from earth bar when ir testing eg testing one circuit .
 
It should be common knowledge really?

This is why the dead tests cannot be completed on an initial verification if the supply has not been introduced.
 
Not to me widdler ive always ir tested with all circuit conductors removed then done relivent tests then done a global test if such as cu change . So if a new circuit was added you would leave l and n out and connect cpc to earth bar and test between ln le ne . Which result do you record on cert seperate circuits or the same global result for all circuits.
 
Last edited by a moderator:

Reply to IR testing ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
758
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
664
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Replies
6
Views
2K
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
589
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock