Search the forum,

Discuss IR Tests & Fault Finding in the UK Electrical Forum area at ElectriciansForums.net

ThreadNecromancer_zps0cd5ba49.jpg
 
Hi fellow electricians,


I'll get straight to the point.
How low do the readings for an IR test need to be on 250V or 500V scale before a 30mA RCD or 32A MCB trips when the circuit is live and in operation and where would I find that information? I know it will trip straight away with a dead short but if I get 50M ohms for example on the dead test and then liven the circuit up is it likely to trip after a certain period of time?
Also why does the RCD or MCB not trip straight away? What factors affect the circuit to the point that the RCD or MCB decides it's time to trip if there is not a dead short and there is no faulty appliance?


Finally, can someone confirm that the best way to find the furthest point on a ring in which to split the circuit in half is the socket with the highest Zs.


All contributions are appreciated
Many thanks

????
:smilielol5:
 
0.26 is normally a neon & 0.23 can be electronic piece of equipment still on the circuit, so if you get a low reading around this point always worth having a further look to see if everything is unplugged.
 
my comments in red.

ohm's law. R=V/I, so R=230/0.03, = 7666.66666667 ohms.

Probably closer to 9Ω (0.009MΩ) as it'll trip below 30mA. Plus at such low resistance it's going to be unlikely that the 9Ω is a stable figure so even if you got a higher figure it may well drop below 9 at some point and trip!

I think you should be ok at 50,000,000Ω (50MΩ) though!
 
Last edited:
You'll have to die first!
Old lass next door to me had Bat Out of Hell for hers! :)

oh, bugger. then i won't be able to listen to it. that is unless technology has improved to send music into another dimension. it could happen now the hadron particle collider is refurbed at double the old speed.
 
Probably closer to 9Ω (0.009MΩ)

I think you meant 9. You have to watch these details because there are lots of people round these parts who'd believe you and start passing systems with 9Ω IR!
 

Reply to IR Tests & Fault Finding in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock