Hi fellow electricians,


I'll get straight to the point.
How low do the readings for an IR test need to be on 250V or 500V scale before a 30mA RCD or 32A MCB trips when the circuit is live and in operation and where would I find that information? I know it will trip straight away with a dead short but if I get 50M ohms for example on the dead test and then liven the circuit up is it likely to trip after a certain period of time?
Also why does the RCD or MCB not trip straight away? What factors affect the circuit to the point that the RCD or MCB decides it's time to trip if there is not a dead short and there is no faulty appliance?


Finally, can someone confirm that the best way to find the furthest point on a ring in which to split the circuit in half is the socket with the highest Zs.


All contributions are appreciated
Many thanks
 
Hi fellow electricians,


I'll get straight to the point.
How low do the readings for an IR test need to be on 250V or 500V scale before a 30mA RCD or 32A MCB trips when the circuit is live and in operation and where would I find that information? I know it will trip straight away with a dead short but if I get 50M ohms for example on the dead test and then liven the circuit up is it likely to trip after a certain period of time?
Also why does the RCD or MCB not trip straight away? What factors affect the circuit to the point that the RCD or MCB decides it's time to trip if there is not a dead short and there is no faulty appliance? ohm's law. R=V/I, so R=230/0.03, = 7666.66666667 ohms.
Finally, can someone confirm that the best way to find the furthest point on a ring in which to split the circuit in half is the socket with the highest Zs. not an exact method. better to dead test the resistance on low ohms.


All contributions are appreciated
Many thanks

my comments in red.
 
i'll ask geordie to lend him his flat cap.
 
Thanks Telectrix, took me a while but I finally got it (I think)
So the results need to be as low as 7.6M ohms before the RCD trips. So if I test a circuit and I get 50M ohms why does it trip after a while?

Not sure if Nickblake and Murdoch are taking the mick...

GGF you're only as good as the experience you've had lol I'll keep testing...
 
not 7.6 meg. 7.667 K. RCD will never trip at 50 Meg. BS 7671 states thatr a reading of 1Meg. is acceptable.
 
no 7666 OHMS not MOhms...
intermittent fault, damp ingress into a light fitting, chafed cable etc etc (had a weird one once, only tripped at random times, checked a light fitting which was alright...looked above...with the torch...copper glinting back in the darkness...socket cable had been damaged through chafing, and everytime someone trod on the floor above the cable it was enough to move the cable and cause the rcd to ping out...)
 
See I was always too embarrassed to ask how many digits in 1 meg, I kinda feel stupid now but I better get it straight before I move on, 1st year stuff I know.
1000 ohms is 1 Kohm? 1,000,000 ohms is 1 Mohm?
So when my meter says >999 M it's greater than 999 million ohms?

Thanks overskilled

I have a megger 1730, I done a fault find today and IR said 0.51 on the ring. After an hour and a half of investigation I found a cupboard behind the f/f with a neon switch in the on position. Turned it off and it took my readings up to 160. So I put everything back together everything still unplugged and switched off and results dropped to 50. So this is why I'm asking these questions. I have to go back and rectify the fault but just wanted confirmation the RCD is not going to trip in the middle of the night.
 
anything over 2 Meg. you can assume to be OK. and them neons are a pain if hidden. anothe fav. for false readings is an aerial amp. in the attic.
 
I'm intrigued. Your website offers a complete range of services including fault-finding, installations, testing, the whole 9 yards. Is this your company? Daz
 
ThreadNecromancer_zps0cd5ba49.jpg
 
Hi fellow electricians,


I'll get straight to the point.
How low do the readings for an IR test need to be on 250V or 500V scale before a 30mA RCD or 32A MCB trips when the circuit is live and in operation and where would I find that information? I know it will trip straight away with a dead short but if I get 50M ohms for example on the dead test and then liven the circuit up is it likely to trip after a certain period of time?
Also why does the RCD or MCB not trip straight away? What factors affect the circuit to the point that the RCD or MCB decides it's time to trip if there is not a dead short and there is no faulty appliance?


Finally, can someone confirm that the best way to find the furthest point on a ring in which to split the circuit in half is the socket with the highest Zs.


All contributions are appreciated
Many thanks

????
:smilielol5:
 
0.26 is normally a neon & 0.23 can be electronic piece of equipment still on the circuit, so if you get a low reading around this point always worth having a further look to see if everything is unplugged.
 
my comments in red.

ohm's law. R=V/I, so R=230/0.03, = 7666.66666667 ohms.

Probably closer to 9Ω (0.009MΩ) as it'll trip below 30mA. Plus at such low resistance it's going to be unlikely that the 9Ω is a stable figure so even if you got a higher figure it may well drop below 9 at some point and trip!

I think you should be ok at 50,000,000Ω (50MΩ) though!
 
Last edited:
You'll have to die first!
Old lass next door to me had Bat Out of Hell for hers! :)

oh, bugger. then i won't be able to listen to it. that is unless technology has improved to send music into another dimension. it could happen now the hadron particle collider is refurbed at double the old speed.
 
Probably closer to 9Ω (0.009MΩ)

I think you meant 9. You have to watch these details because there are lots of people round these parts who'd believe you and start passing systems with 9Ω IR!
 

Reply to IR Tests & Fault Finding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
438
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top