Is a borrowed earth allowed?

Discuss Is a borrowed earth allowed? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
138
Done an EICR yday on an old house and all ok apart from 2 issues..
1) 32A cooker circuit had high resistance pec continuity (over2kohms) ALTHO it did buzz out on my voltage probes. Hence not able to get a Zs reading and no rcd tripping. The dual rcd consumer unit was fitted 10 yrs ago and those test readings all available and fine. Kitchen was refitted 3 yrs ago and no docs available so they extended original cooker cable prob from the switch which is now tiled over somewhere.
.. I've put in an earth wire link from an immediately adjacent rfc socket into the cooker switch and this solves this problem.
Question .. is this ok as a permanent solution if i label up what ive done?
2) lowish IR readings 1.75M L-E and N-E on light circuits and one rfc but possibly in hindsight due to some bulbs, fan and appliances still plugged in. Could this account for it?
 
Not right now Westy, but go ahead fill yer boots
What I am saying is that he has done nothing wrong, it is permitted provided it is adequate for a cpc to serve more than one circuit. What he has done may seem unorthodox but I was asking for those who disagree with his actions to back it up with a Regulation.
 
What I am saying is that he has done nothing wrong, it is permitted provided it is adequate for a cpc to serve more than one circuit. What he has done may seem unorthodox but I was asking for those who disagree with his actions to back it up with a Regulation.
Ah right, I don't have a copy of BS 7671, so in all honesty I can't confirm if there is a regulation.
 
Anyone want to quote a Regulation where this is not permitted providing the borrowed cpc is adequate for fault protection requirements.
Question - what is the state of the cpc for the cable, along its length? Cables in walls 522.6.202 has me thinking about a screw being driven into the cable. If CPC is 2K then it should be sufficient to trip a 30mA RCD but the screw may exceed the 50V max target (1667 Ohms).
 
Ok I give up, I'm orrffh to cook a curry is my excuse.

My thoughts were that the cpc must remain effective throughout the life of the install. Therefore, if the RFC is altered or removed subsequently, the installer altering/removing may not know the other circuit is reliant on its cpc.
You could argue if the problem cpc has only one break it is now effectively connected to earth from either end. I think it would be prudent to fit some form of info at the CU.
 
I agree with Westy, the circuits cannot now be independently isolated, anyone working on the RFC in the future could potentially get a shock from the cooker circuit in the event of a fault on the cooker.
It is as BL says like borrowing a neutral, as soon as that link is disconnected there could be a potential difference between the two earth conductors.
Big problem with temporary repairs is that they have a nasty habit of become permanent repairs!
Also, what has now been done must surely screw the test results for the RFC, so how do you document that in the EICR?
Correct thing to do would be to isolate the cooker circuit and label it saying it is not to be used until remedial action has been carried out and document that to the client.
 
2) lowish IR readings 1.75M L-E and N-E on light circuits and one rfc but possibly in hindsight due to some bulbs, fan and appliances still plugged in. Could this account for it?
If you got those readings of the same lighting circuit, then I would say there is a fault on that circuit. Did you disconnect the earth and neutral for that circuit out of the board before testing?
 
As some of the more experienced have said... It is fine to use a CPC common to two or more circuits, and it complies with a regulation 543.1.2 (as long as it's CSA is sufficient).

I do find it worrying when members, some are even trusted members, give the wrong advice and give it out so quickly without giving proper thought. We all get it wrong at times, but at least lets give it some thought before we get it wrong.
 

Reply to Is a borrowed earth allowed? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock