Discuss Is a borrowed earth allowed? in the UK Electrical Forum area at ElectriciansForums.net

Funnily enough, I made a similar mistake a couple months ago.. I put in a socket spur from a socket on the rfc which was being covered over.. after plasterer had been I retested and found there wad no earth at new socket! I had to cut out an inspection hole and found the new cpc had actually snapped off inside the terminal for some reason (possibly a hurried stripping operation).. so it DOES happen!
 
Hope it wasn't one of these;
IMG_2024.JPG
 
There are other concerns too..maybe there could be another radial in the kitchen with a 'lost ' earth and the previous spark has already borrowed the cooker earth......So new cooker circuit in /old cooker circuit out might leave another circuit unprotected...Full test might identify that..I suppise...I dont really see a problem with just installing a new separate earth..Why does it need to be in the same cable.
 
Funnily enough, I made a similar mistake a couple months ago.. I put in a socket spur from a socket on the rfc which was being covered over.. after plasterer had been I retested and found there wad no earth at new socket! I had to cut out an inspection hole and found the new cpc had actually snapped off inside the terminal for some reason (possibly a hurried stripping operation).. so it DOES happen!

GASP!
 
Sorry this is late, I only usually look once a week when the summary comes around. I have carried quite a few 'serious' Grounding / Earthing related works in the past. In one case, in a very large shopping and business complex in the upper Midlands, with its own substation in the basement, I determined (and they eventually admitted after legal pressure) that they had failed !!!!! to reconnect the Earth to the whole building after they had tested and commissioned the substation! So much for the "professionals" in the DNO's.

Another case was a multiply-supplied (with originally 6 separate meters) industrial/scientific starter-unit complex (with a different DNO) that eventually had one pharmaceutical owner and had really high EMF magnetic fields in their labs (like 50 microteslas) from stray currents which were affecting the biological research results. I determined what the problem was. It was in the local distribution network and not their own supply cables. The only way to sort it was to remove all but one of the network protective Earths and rely on that and the buildings steel structures into the ground (like super Earth Rods). That sorted the problem and the DNO agreed with me that it was the only practical solution. So we did that BUT also affixed signed warning notices at all the incoming supply points to say what we had done in some detail and why.

I agree with SparkyChic that ideally the CPC should be of adequate size, but, if as you say, it is a dual RCD protected installation then all any CPC needs to carry will be 30 mA (or possibly 100 mA). This is not yet reflected in BS7571 - even in the latest 18th Edition.

I think, if you leave it that way, you should stick a notice near the CU saying that is what you have done. It should be safe, but it should not be un-noted. I would have done what you did.
 
Sorry this is late, I only usually look once a week when the summary comes around. I have carried quite a few 'serious' Grounding / Earthing related works in the past. In one case, in a very large shopping and business complex in the upper Midlands, with its own substation in the basement, I determined (and they eventually admitted after legal pressure) that they had failed !!!!! to reconnect the Earth to the whole building after they had tested and commissioned the substation! So much for the "professionals" in the DNO's.

Another case was a multiply-supplied (with originally 6 separate meters) industrial/scientific starter-unit complex (with a different DNO) that eventually had one pharmaceutical owner and had really high EMF magnetic fields in their labs (like 50 microteslas) from stray currents which were affecting the biological research results. I determined what the problem was. It was in the local distribution network and not their own supply cables. The only way to sort it was to remove all but one of the network protective Earths and rely on that and the buildings steel structures into the ground (like super Earth Rods). That sorted the problem and the DNO agreed with me that it was the only practical solution. So we did that BUT also affixed signed warning notices at all the incoming supply points to say what we had done in some detail and why.

I agree with SparkyChic that ideally the CPC should be of adequate size, but, if as you say, it is a dual RCD protected installation then all any CPC needs to carry will be 30 mA (or possibly 100 mA). This is not yet reflected in BS7571 - even in the latest 18th Edition.

I think, if you leave it that way, you should stick a notice near the CU saying that is what you have done. It should be safe, but it should not be un-noted. I would have done what you did.

The secod one was was due to PME problems in the area.
 
I would say that borrowed earths are not good practice ……..one alternative may have been to run a separate 4 0r 6mm cpc back to the consumer unit.
I don't think anybody is arguing that it is good practice. The op was about whether it was an acceptable alternative in the circumstances he/she faced. If you are going to the trouble of running a new single cpc back to the CU, I suspect in this case you may as well run in a new twin & earth.
 
New posts

Reply to Is a borrowed earth allowed? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
664
Good evening all, So been to an upstairs flat today I East ham, the entire road is terraced 2 storey building which look like a row of terraced...
Replies
9
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
870
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock