Hi Guys,

I've just been looking at a job that has been installed by another company.
One thing I've noticed are the feeds to 2 BMS / Plant panels. They have run in 2 x 150mm 4C and doubled up on the main switch in both panels. No separate CPC has been installed and the banjos aren't earthed either.
If this had been myself I'd have run in a separate CPC and bonded the Banjos.
Thoughts please is this to regs or does it need a separate CPC ?
 

Attachments

  • 20221021_130035.jpg
    284.7 KB · Views: 26
  • 20221021_130030.jpg
    395.6 KB · Views: 26
It is unlikely to need a seperate CPC, you need to do the calculation to confirm that though, it is impossible to tell from looking at it. The armour of SWA, especially with 2 in parallel is likely to be suitable as the CPC.

The connection to the banjo doesn't look too good however, they should have at least cleaned the paint off the metal where the bolt connects to it.
What is on the outside of the enclosure? Is the gland and banjo fitted to clean metal on that side?
 
Is the wire armour earthed the other end?
Might they have used the adiabatic equation (as the armour of 150 sq mm 4c SWA is only 73 sq mm equivalent copper)?
Is the body of the cabinet being used?
What are the earthing requirements of the load?
 
It is unlikely to need a seperate CPC, you need to do the calculation to confirm that though, it is impossible to tell from looking at it. The armour of SWA, especially with 2 in parallel is likely to be suitable as the CPC.

The connection to the banjo doesn't look too good however, they should have at least cleaned the paint off the metal where the bolt connects to it.
What is on the outside of the enclosure? Is the gland and banjo fitted to clean metal on that side?

Hi, the outside is the same as the inside, fully painted. They've just drilled the plate and bolted it down.
 
Is the wire armour earthed the other end?
Might they have used the adiabatic equation (as the armour of 150 sq mm 4c SWA is only 73 sq mm equivalent copper)?
Is the body of the cabinet being used?
What are the earthing requirements of the load?

Not that I'm aware of.
The cabinet is being used as the earth for outgoing Services connected to din mounted earth terminals.
 

Reply to Is a separate CPC required ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
537
Has anyone fitted an SPD to a schneider standalone AFDD DB. Isobar P B Standalone Active distribution board, Acti9, 24 AFDD ways This board only...
Replies
4
Views
833
Hello all. I have just bought my first house but it needs a bit of work. I am re-wiring it and I've found the conservatory ring has been spurred...
Replies
11
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
848

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock