Jules123

DIY
Reaction score
7
An electrician has recently quoted to replace our old oven. He says that the new oven has different power requirements and he needs to replace the consumer unit to make this lower and avoid burning out our new oven within weeks! The cu was new in 2015 so I am concerned that it now needs replacing - this will cost double the cost of the oven... Help please!
 
him talk with forked tongue. if there isno spare waysin the existing CU for the cookwer, then a singleway unit could be instaaled, splittong the feed taitsfrom the metaer/isolator.
 
I can’t see why it would need lowering and require a new Consumer Unit , the oven will only draw as much current as it requires .ohms law demands this at the same voltage
 
An electrician has recently quoted to replace our old oven. He says that the new oven has different power requirements and he needs to replace the consumer unit to make this lower and avoid burning out our new oven within weeks! The cu was new in 2015 so I am concerned that it now needs replacing - this will cost double the cost of the oven... Help please!

Welcome to the forum.
I'm not as polite as the others and will say that it sounds like the electrician is talking rubbish.... or you may have misheard them.
Get the electrician to put a his explanations in writing and then post that up on here.
 
Welcome to the forum.
I'm not as polite as the others and will say that it sounds like the electrician is talking rubbish.... or you may have misheard them.
Get the electrician to put a his explanations in writing and then post that up on here.
Thanks. It's only a Hotpoint oven. I'll ask about the reason for a new CU.
 
Worst case scenario a new smaller cu (1 way) can be installed for oven. Can't see any situation where a 2015 board would need changed for the sake of an oven.
Perhaps he only meant part of the board but has quoted around £400 for part and to fit...does that sound right?? Along with other work quoted separately...thanks for your advice
 
It really depends on your location as prices vary massively across the country. I wouldn't expect a full board change to be as little as 400 so it could be for a new separate board. Probably best to get a little more detail off him first.
 

Reply to Is new cu required for new oven install? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
736
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
My Lamona oven has broke so I’m replacing it with a new one. Does it matter that the new one I’m wanting to get is 2.8kw compared to the current...
Replies
2
Views
520
Hello all, I'm in the process of having my kitchen refurbished and I'm looking for advice on my current setup as I have been told that I will...
Replies
15
Views
4K
Hi all, I replaced my old Electrolux oven which operated with a 13 amp plug. The new Kenwood oven I ordered says a 16 amp (Requires hardwiring to...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock