Discuss Is new cu required for new oven install? in the UK Electrical Forum area at ElectriciansForums.net

He said something about old being 40 and new only being 20. Both are hard wired but the position isn't changing. He said the new one would burn out due to the difference...images attached.

So the old cooker is connected to a 40A breaker and the new one only needs a 20A breaker.?? Is this correct?

I'd consider getting another electrician in to quote for the job...
Maybe there is an electrician on the forum that lives near you (High Wycombe) that could give you a quote.
 
An electrician has recently quoted to replace our old oven. He says that the new oven has different power requirements and he needs to replace the consumer unit to make this lower and avoid burning out our new oven within weeks! The cu was new in 2015 so I am concerned that it now needs replacing - this will cost double the cost of the oven... Help please!
BS. The appliance draws power it's not pushed into it! Totally fraudulent to suggest what he is saying. If it's lower power fine just connect up the new oven. BTW. Its worth checking if he is a registered electrician and wether he has a CPS no. Find out and notify his competent persons scheme, NAPIT, NICEIC etc. Let them know what he is up to.
 
An electrician has recently quoted to replace our old oven. He says that the new oven has different power requirements and he needs to replace the consumer unit to make this lower and avoid burning out our new oven within weeks! The cu was new in 2015 so I am concerned that it now needs replacing - this will cost double the cost of the oven... Help please!

He's either lying or totally incompetent!

If the new oven is only 20A than the MAXIMUM it can draw is 20A.

It doesn't matter that the supply is suitable for up to 40A, the oven can only draw up to 20A .

This is pretty basic stuff for an electrician!

So, regulations:
Since the oven is known as a fixed load in electrical terms, the existing 40A supply can remain as is without the need to change it - merely connect the new oven. (Although if I had a suitable smaller MCB closer to 20A I would probably change it - but it isn't mandatory)

However, it may be the case that your existing installation doesn't have RCDs (although given the age it should) in which case it should be upgraded - for more than the oven!)

Do you have a photo of the board?
 
He said something about old being 40 and new only being 20. Both are hard wired but the position isn't changing. He said the new one would burn out due to the difference.

OK, it sounds like you have an oven circuit which is currently protected by a 40A MCB and the new oven probably requires a 20A supply, this is likely to be specified in the manufacturers instructions.

Connecting the new oven to the existing 40A supply will not cause it to burn out, this is just not possible.
It is possible that the electrician who has told you this simply doesn't understand the basic science of electricity and genuinely believes that what they are saying is true (this is true for a scary number of people trading as electricians these days) or else they are outright trying to scam you.

Whilst technically it is acceptable to connect the new oven to the existing supply as-is there may be advantages to changing the 40A circuit breaker to a 20A one, but this would not require the whole CU (fusebox) to be replaced! It would only require the one circuit breaker to be replaced, even if it is not RCD protected currently then a circuit breaker which incorporates RCD protection, called an RCBO, could be fitted.


However if there is a genuine reason to advise replacing the CU then any decent electrician would explain this properly along with explaining what the improvent would be and why you might need them.
 
Echoing the sentiment of most posts above, i think we can agree in summary that it is the electrician that needs replacing, not the distribution board.

following the absurd explanation about a 40A supply burning out a 20A oven in weeks, its incredible that we have all survived the change to led "light bulbs" as they generally use about 90% of the power. so an original 6A lighting circuit should be burning out the new lights within minutes!! :) ;)
 
So the old cooker is connected to a 40A breaker and the new one only needs a 20A breaker.?? Is this correct?

I'd consider getting another electrician in to quote for the job...
Maybe there is an electrician on the forum that lives near you (High Wycombe) that could give you a quote.
Thanks for replies everyone. Looks like we need to keep looking for an electrician! Had two quote so far and need someone for some kitchen electrics as cowboy kitchen fitters had to be let-go. They were damaging the units! Dream kitchen not going so well atm 😟
 
He's either lying or totally incompetent!

If the new oven is only 20A than the MAXIMUM it can draw is 20A.

It doesn't matter that the supply is suitable for up to 40A, the oven can only draw up to 20A .

This is pretty basic stuff for an electrician!

So, regulations:
Since the oven is known as a fixed load in electrical terms, the existing 40A supply can remain as is without the need to change it - merely connect the new oven. (Although if I had a suitable smaller MCB closer to 20A I would probably change it - but it isn't mandatory)

However, it may be the case that your existing installation doesn't have RCDs (although given the age it should) in which case it should be upgraded - for more than the oven!)

Do you have a photo of the board?
Screenshot_20230228-194804_Gallery.jpg

Thanks for replies everyone. Looks like we need to keep looking for an electrician! Had two quote so far and need someone for some kitchen electrics as cowboy kitchen fitters had to be let-go. They were damaging the units! Dream kitchen not going so well atm 😟
He said it only had one rcd??
 

Reply to Is new cu required for new oven install? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
742
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
My Lamona oven has broke so I’m replacing it with a new one. Does it matter that the new one I’m wanting to get is 2.8kw compared to the current...
Replies
2
Views
522
Hello all, I'm in the process of having my kitchen refurbished and I'm looking for advice on my current setup as I have been told that I will...
Replies
15
Views
4K
Hi all, I replaced my old Electrolux oven which operated with a 13 amp plug. The new Kenwood oven I ordered says a 16 amp (Requires hardwiring to...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top