Discuss Is new cu required for new oven install? in the UK Electrical Forum area at ElectriciansForums.net

Don't think your images worked. Copy and paste works well on this forum for images by the way.

Even if not RCD protected I'd still change a broken appliance.
New oven is 4.7Kw. A 'standard' 6 sq mm cable and B32 cooker circuit would be fine. Subject to seeing pictures, it sounds like you should find a different electrician.
 
View attachment 106475

He said it only had one rcd??

There are 2 RCDs in that unit, they are the two devices labelled as RCCB.

Whilst I tried to give some benefit of the doubt earlier I would say this confirms you have been outright lied to.

I see no reason why that 40A MCB couldn't simply be swapped for a 20A MCB if that is required, those MCB's are current and still available.

There may be some mention of that CU being plastic when these days we are required to fit metal ones, but that would not prevent the work as you have described it from being carried out.
 
There are 2 RCDs in that unit, they are the two devices labelled as RCCB.

Whilst I tried to give some benefit of the doubt earlier I would say this confirms you have been outright lied to.

I see no reason why that 40A MCB couldn't simply be swapped for a 20A MCB if that is required, those MCB's are current and still available.

There may be some mention of that CU being plastic when these days we are required to fit metal ones, but that would not prevent the work as you have described it from

I am having the worse time with incompetent traders atm so glad you guys have all taken the time to tell me what's what. Thought it was bizarre that a replacement oven was such a problem!...
 
View attachment 106475

He said it only had one rcd??

Nothing wrong with that consumer unit. (ish)

It has two RCDs!

He can't even count.

You could get the 40A MCB changed to a 20A or 25A, they are available if you want.


Now, it is the case that that consumer unit does not meet current standards, but in itself that doesn't mean it has to be changed.

If there is any sign of heat damage and/or a couple of other things, then it should be changed.

But from your photos, there is no evidence that a change is mandatory.
 
The rules have changed since your CU was installed. Yours is plastic, and only steel ones can be fitted in domestic properties now, but the rules aren't retrospective, so as long as individual parts are available for it (which they are) it doesn't need to be changed.
 
Nothing wrong with that consumer unit. (ish)

It has two RCDs!

He can't even count.

You could get the 40A MCB changed to a 20A or 25A, they are available if you want.


Now, it is the case that that consumer unit does not meet current standards, but in itself that doesn't mean it has to be changed.

If there is any sign of heat damage and/or a couple of other things, then it should be changed.

But from your photos, there is no evidence that a change is mandatory.
Thanks so much for your time Julie! Super helpful 👍
 

Reply to Is new cu required for new oven install? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
742
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
My Lamona oven has broke so I’m replacing it with a new one. Does it matter that the new one I’m wanting to get is 2.8kw compared to the current...
Replies
2
Views
521
Hello all, I'm in the process of having my kitchen refurbished and I'm looking for advice on my current setup as I have been told that I will...
Replies
15
Views
4K
Hi all, I replaced my old Electrolux oven which operated with a 13 amp plug. The new Kenwood oven I ordered says a 16 amp (Requires hardwiring to...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock