I was asked to fix a messed up ring. The client doesn't want to tear apart everything and asked if it will comply with the regs if it is done like this - Let's say we have a ring with three points and a spur from each point. The point is that the three points on the ring will be actually three junction boxes (all accessible) and from each one there will be a run/spur to where the socket outlet will be.
It looks weird to me and not sure if I want to do it, but I can't see why it can't be done! I don't have so extensive experience like you all guys, so any thoughts will be appreciated!

Cheers
 
as long as each unfused spur has only 1 socket outlet on each, then it complies.
 
i've always got mine to hand,

is.jpg
 
Hi everyone,

I was asked to fix a messed up ring. The client doesn't want to tear apart everything and asked if it will comply with the regs if it is done like this - Let's say we have a ring with three points and a spur from each point. The point is that the three points on the ring will be actually three junction boxes (all accessible) and from each one there will be a run/spur to where the socket outlet will be.
It looks weird to me and not sure if I want to do it, but I can't see why it can't be done! I don't have so extensive experience like you all guys, so any thoughts will be appreciated!

Cheers

Sounds like it was wired by a Pole
 
i did advance from it 30 years ago to this:

dan dare vs the mekons, great stiuff.

Eagle_1950_issue_1_front_page.jpg
 
Thanks guys. Yes, I'll do it myself. Yes, I do have a regs book. Yes, I thought about 1/more socket outlets ..... I feel embarrassed.. really embarrassed! Just opened to check the regs again and I saw the answer of my question was in front of my eyes! Basically I can suggest, depending of the location of these junction position that these can be FCUs and he can use double socket if he wants!

Thank you guys and sorry for wasting your time!

PS: :) well I don't know who did the installation, but he says that the whole house was done on one circuit breaker, having a ring to one big junction box and from there runs to each socket outlet!!!
 
Last edited by a moderator:
don't be embarrased to ask questions if you are still on a learning curve, as your screen name suggests. that's what us old farts are here for---- to help the young sprogs get it right. :90:
 
Hi Let's say we have a ring with three points and a spur from each point. The point is that the three points on the ring will be actually three junction boxes (all accessible) and from each one there will be a run/spur to where the socket outlet will be.

No that doesn't comply, you cannot have more spurs than you have points on the ring. As you have no points on the ring you cannot have any spurs.

What exactly is the situation now and what have you been asked to do?

For only 3 twin sockets you could just make it a 20A radial.


Once upon a time, when the ring final circuit was new, the above joint boxes was how it was often installed. But then the iee put a stop to it sometime in the 13th/14th edition era
 
I'm interested why they put a stop to that method Dave? It would still have the same balanced current across the two legs of the supply, topographically it's still a ring final in that respect even to the point that if the junction boxes were sockets it would be compliant.
 
Yes, I thought about that and as there will be just a few points I will suggest to him to use FCUs instead of junction boxes. This way will be fine.

The existing one was one ring for the whole house with just one big junction box on it and from there you have spurs to each location.

PS: Wasn't there a reg about length of the spur? I think there was something about no more than 3m, but I can't find it to double check that, so I may be wrong!
 
Yes, I thought about that and as there will be just a few points I will suggest to him to use FCUs instead of junction boxes. This way will be fine.

The existing one was one ring for the whole house with just one big junction box on it and from there you have spurs to each location.

PS: Wasn't there a reg about length of the spur? I think there was something about no more than 3m, but I can't find it to double check that, so I may be wrong!

Where will these FCUs be? That sounds like an even worse idea!

How can it be a ring if it had a big JB with spurs to each point?
 
I'm interested why they put a stop to that method Dave? It would still have the same balanced current across the two legs of the supply, topographically it's still a ring final in that respect even to the point that if the junction boxes were sockets it would be compliant.

Buggered if I know, I wasn't even born then!
 
This is how it was described to me. I don't know how do you call a ring with one point and radials from that point!?
He says these junction points will be accessible - I haven't been there yet so I don't know if it will be in a floor box or somewhere else!
 
This is how it was described to me. I don't know how do you call a ring with one point and radials from that point!?
He says these junction points will be accessible - I haven't been there yet so I don't know if it will be a floor box or somewhere else!

It can't be a ring if it only has one point! It's more likely to be an old spider type radial circuit.

What exactly is going on here?
 
This is how it was described to me. I don't know how do you call a ring with one point and radials from that point!?
He says these junction points will be accessible - I haven't been there yet so I don't know if it will be in a floor box or somewhere else!

Scary stuff. Best you go and see this first hand......
 
I don't know. This is why I was asked to fix it!

Yes, I will go first to take a look before I start. He's far from me, so I'm getting as much info as I can before my visit!
 
Last edited by a moderator:
Sounds like a Spider ring or radial.
If it covers more than one floor, most likely a ring.
Don't take any notice of the one spur per point myth, as it's just a myth.
Spurs can be taken from any point on a ring, including the CU, as shown in Appendix 15.
 
1 unfused spur per socket and unlimited per fused spur, or am I on the 19th edition?

You have to be careful with the wording. One unfused spur per socket implies that spurs can only be taken from a socket.
Wheras what is meant is that you cannot have more unfused spurs than you have points on the ring.
 
I'm not sure I'd want every socket in the house to be on a fused spur with a 13A fuse upstream of it. Daisy-chaining points behind a fused spur avoids any question of cable overload but it's not good practice and doesn't make the CCC of the ring available throughout which is the main idea.

I'm interested why they put a stop to that method Dave? It would still have the same balanced current across the two legs of the supply, topographically it's still a ring final in that respect even to the point that if the junction boxes were sockets it would be compliant.

I've always though that the main point of this is to encourage installers to run the ring around most of the floor area of the premises. Otherwise there might be all sorts of haphazard layouts, e.g. a small ring around a central area with spurs heading out to do most of the work - a kind of extreme spider ring - or a long thin ring along one side and spurs across. There was a period when old radial installations were being modernised with rings and the temptation would have been to re-purpose the radials as spurs. This defeats the main advantages of the RFC - to enable full capacity to be used almost anywhere and to allow easy expansion by breaking into the ring.

There is also the aspect that if you use actual points at the spur tap-off locations, they will attract some of the loading from the ends of the spurs.
 
Spider rings comply, but are rather impractical.
Spurs cannot be taken from existing sockets, as they are already Spurs.
They involve JBs invariably under floor boards which since the advent of fitted carpets are virtually inaccessible, and especially so now with the trend for laminate flooring.
 

Reply to Is this considered ring in general and/or by the regs? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, client wants some sockets and 20a switches moved into high cupboards in kitchen and above 1200mm for tvs etc, the apartment was built in 2016...
Replies
11
Views
1K
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
810
HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
Replies
18
Views
4K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
682

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock