Discuss Is this installation considered acceptable today? (1-ring including oven and everything else) in the UK Electrical Forum area at ElectriciansForums.net

I meant just a sly peek over the shoulder as you pass him a cup of tea, not CCTV surveillance.
You'll have to tell him he's being recorded.

If you would be so kind as to tell us the answers to these questions after he's been:-
1. Does electrician take the cover off the board?
2. Does he use a test kit or multi-function tester at all?
3. Does he leave within an hour?
We'll be able to say how competent (or lazy) the electrician is

Problem is, the LL doesn't have to act on the EICR unless there's some serious (dangerous) problems, and if he does, it could take months for any changes
 
If there are two rings discovered inside the CU terminated into one MCB it may well be that DIY tampering has been at work since the EICR. BUT if only one is discovered the person who wrote up the EICR should be fired, I do wonder if there are a number of flats at the OPs location of the same size and layout and creative guesswork has been utilised rather than proper inspection and testing ?
If I tested a property with just a single ring final circuit and an electric oven was also on that circuit I'd definitely flag it up as a C3 - Improvement recommended.
 
I meant just a sly peek over the shoulder as you pass him a cup of tea, not CCTV surveillance.
You'll have to tell him he's being recorded.

If you would be so kind as to tell us the answers to these questions after he's been:-
1. Does electrician take the cover off the board?
2. Does he use a test kit or multi-function tester at all?
3. Does he leave within an hour?
We'll be able to say how competent (or lazy) the electrician is

Problem is, the LL doesn't have to act on the EICR unless there's some serious (dangerous) problems, and if he does, it could take months for any changes

I would add that I didn't put this in place for this occasion!

The CU is in the hallway to the left of the entrance door hence its covered so well by existing CCTV covering the entrance.

I will advise the guy that he may be recorded and kept for 48 hours. My only thought was this could be handy to show you guys what is found inside the CU, but absolutely no intent to show the poor spark who's probably never had anything to do with this property.

(Don't think that would be OK to do anyway and I am registered with the ICO as a data controller for the CCTV system so I take my responsibilities there seriously.)

If the guy doesn't take the cover off the board I can say I'll be moving out...

If there are two rings discovered inside the CU terminated into one MCB it may well be that DIY tampering has been at work since the EICR. BUT if only one is discovered the person who wrote up the EICR should be fired, I do wonder if there are a number of flats at the OPs location of the same size and layout and creative guesswork has been utilised rather than proper inspection and testing ?
If I tested a property with just a single ring final circuit and an electric oven was also on that circuit I'd definitely flag it up as a C3 - Improvement recommended.

It does have the name of the person signing off on the EICR on the report so I could follow up further if needed once this has taken place.

I've scanned a copy of this before anyone requests seeing it tomorrow so that I definitely have a copy.

The only C3s listed are:

1. Smoke alarms wired in 3core flex earth wire used as live [Christ?! Thankfully its not T&E!]
2. Circuit chart not marked
3. Only partial RCD protection [Doesn't cover the half with lighting circuits and 16A radial]
4. 4.9 Correct identification of circuit details and protective devices (514.8.1; 514.9.1) is recommended for improvement
5. 4.10 Presence of RCD quarterly test notice at or near consumer unit/distribution board (514.12.2) is recommended for improvement
6. 4.11 Presence of non-standard (mixed) cable colour warning notice at or near consumer unit/distribution board (514.14) is recommended for improvement.
7. 4.18 RCD(s) provided for fault protection - includes RCBOs (411.4.9; 411.5.2; 531.2) is recommended for improvement.
8. 4.19 RCD(s) provided for additional protection - includes RCBOs (411.3.3; 415.1) is recommended for improvement
9. 5.12.3 For cables connected in walls at a depth of less than 50mm (522.6.202; 522.6.203) is recommended for improvement.
10. 5.12.4 For cables concealed in walls/partitions containing metal parts regardless of depth (522.6.203) is recommended for improvement.
11. 8.1 Additional protection for all low voltage (LV) circuits by RCD not exceeding 30mA (701.411.3.3) is recommended for improvement.
 
Last edited:
ref #83,
point 1,- is just unbelievable. Have you checked your detectors work? and if more than one, are they interconnected? All sound when one tested? What is the "replace by" date on them?

point 2,- Could have been done when the EICR was carried out.

point 3,- pointless. Not all circuits have to be RCD protected.

point 4,- See point 2

point 5,- Pure laziness. You get a sticker with every RCD in the box.

point 6,- Only needed if there are mixed colours in the installation.
(ok, I guess there is if the detectors are wired in flex!)

points 7 to 11 are just spouting off regulations as far as I can see to cover earlier points
 
If there are two rings discovered inside the CU terminated into one MCB it may well be that DIY tampering has been at work since the EICR. BUT if only one is discovered the person who wrote up the EICR should be fired, I do wonder if there are a number of flats at the OPs location of the same size and layout and creative guesswork has been utilised rather than proper inspection and testing ?
If I tested a property with just a single ring final circuit and an electric oven was also on that circuit I'd definitely flag it up as a C3 - Improvement recommended.
Dave OCD, I half agree in so far as I would flag it as an observation only with no code.

In EICR's I use the codes C1, C2, C3, FI as per guidance, but I also put in observations as no code.

Aluminium cables that have good test reads I put under observation only no code.
Re wire able fuse boards observation only no code.

There are some things I find that I personally don't like ,but I have no right to go against regs and code them, so I make a comment with an explanation with no code observation only.
I make it clear to customer than no action is required on these points and I am only highlighting issues I would personally advise to upgrade.
 
You’ll know if they’re not a good electrician, they’ll walk out when you tell them they’re being recorded!

Do you need to tell them? Your not a business.
Hi - hopefully I am a thorough and competent person with the experience, training and skills to carry out a domestic report as required here. I would not proceed with work being recorded for forensic examination and judgement by persons unknown to me. Why would I?
 
So the electricians, two of, have been out this morning and arrived bang on 9am as arranged.

Arrived with a toolkit and a Fluke 1653.

Didn’t want any tea or coffee.

First thing I said on their coming into the door are there are two CCTV cameras pointing right at you here and here.

First thing they did was open up the CU with a screw driver and have a look at the cabling. No isolation and no dead test (obviously, it wasn’t dead).

They identified only one ring, 6mm2 on the next B32 to the shower and 10mm2 on the non-functional B40.

I said this went against the September 2017 EICR which I presented and they looked it over.

The guy who had opened the CU then commented this has not been done on this board.

There was talk about this being raised with the guy that did the testing.

They ran round with the Fluke doing some tests in a few sockets on the ring and then discussed my concerns that had brought this to light.

They advised me that my LA typically are happy with trainee sparks opening up the CU and running new lines in their experience, however, I asked for a quote for them to assist me running a radial to the PC setup and they quoted £120 for labour and testing. I have all materials there.

I want to double check the trunking factors but I think what I have should be fine.

So Murdoch it looks like you were on the money. EICR completely fabricated and probably the only legitimate concerns are that the installation wasn’t tested.

P.S. smoke alarms aren’t wired as Earth for live, at least not now, the earth is just snipped in the 3core and they’re not earthed. Live is brown and neutral blue though.

Edit: total visit time was around 40 minutes.
 
Last edited:
I'd forget the cctv observation -not many tradespeople are going to appreciate that even if they are good ones.

Just ask if you can take some photos. He/she shouldn't have a problem with that. And photos will be clearer than cctv footage anyway.
 
Re the smoke alarms .... You say the earth is snipped ...... All mains circuits need a continuous cpc from the board to the end of circuit.

How are they interlinked? This isn't an EICR matter btw.
 
I'm guessing that the smoke alarms should be earthed, although they're plastic bodies into plastic shells so maybe double insulation is acceptable, I'm unsure of their model so can't say without looking into it further.

It looks like the bodies can be twisted and removed, so I'll see if I can at least get a model number to look into them further.

They're connected from a 6A MCB into a switched spur which is then connected on to the smoke alarms. Trunking runs from the output of the spur to each of the smoke alarms.

Testing them, they all go off. All of them except one displays a green LED when the MCB is on.

They are interlinked, takes a second or two for them to all start going so I wondered if it was perhaps a wireless signal interlinking them.

If the 3core has been reduced to two core, which seems to be the case, I'd imagine that they must be wirelessly interlinked to operate.

That may also explain the terrible WiFi signal in my house.
 
Hi - pretty sure the alarms are 860mHz and only transmit when they've something to report, so they're unlikely to affect your WiFi. If you'd like to try it, turn off your CCTV (recorder and everything) and see if that improves the WiFi throughput :) .
 
Hi - pretty sure the alarms are 860mHz and only transmit when they've something to report, so they're unlikely to affect your WiFi. If you'd like to try it, turn off your CCTV (recorder and everything) and see if that improves the WiFi throughput :) .

Good to know, so that signal is not going to be even close to WiFi - and longer range which makes sense for safety devices.

I found the WiFi to be dire even before the CCTV got added in, but it definitely adds strain to it!

The solution I came to was to put an AP in the lounge and an AP in the master bedroom, pretty much opposite ends of the house, and it works pretty well.

If I continue to have issue, may split the network for the CCTV and the rest, but I'm in the process of running 12x CAT6 to each room so the WiFi really is non critical for anything intensive by the time I'm done.
 

Reply to Is this installation considered acceptable today? (1-ring including oven and everything else) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
705
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
853
Hello Electrical world. Looking for thoughts and opinions. Currently planning out my kitchen re-wire for new kitchen. I was originally...
Replies
13
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock