Hi all hope you can help me on this one as heating is not my forteit. Got a communal heating system 6 flats one heating system. 5 flats have heat 1 doesn't. Plumber been to it and says its electrical as no power to the controller. Each flat has it's own controller fed locally from their own board. Each flat has it's own port valve in the plant room boiler and stats etc. There is also a bank of relays but not dont know what they do.Any help will be helpful guys
 

Attachments

  • IMG-20201007-WA0000.jpg
    119.1 KB · Views: 22
I'm assuming that the relay circled is for the problem flat
The relay on the left does not look to be used the other relays look to be a common switch to run the heating with each relay being energised from the corresponding flat controls and supply
First off you need to check that when the flat calls for heat that power is getting to the relay
Given that the relay on the left does not appear to be used I would use it as a known good swap for a possible faulty relay
 
In the absence of any drawings or other information the way I envisage it working each flat will energise one of the relays that will then operate the corresponding motorised valve which will fire the boiler and run the pump
It looks like that relay panel is just to provide supply isolation / separation between each of the flats heating controls and the heating equipment
 

Reply to Issue with heating controls in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
951
Hi. I'm installing a wet underfloor heating system in my own house. What would you recommend as the best smart control system? I can hardwire...
Replies
3
Views
645
Good afternoon chaps, I have an Alpha E-Tec 33 combi boiler (with Google Nest 3rd Gen thermostat) that occasionally fails to put out hot water...
Replies
10
Views
959
Hi everyone, my house has an air-to-heat system that generates hot water in a boiler. This boiler is then connected to the central heating...
Replies
1
Views
814
I have 2 Mira dual valve vision showers. The remote control.for the Vision model has been discontinued, so I bought a Mira Platinum dual...
Replies
0
Views
195

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock