Currently reading:
Keep getting electric shocks in kitchen.

Discuss Keep getting electric shocks in kitchen. in the UK Electrical Forum area at ElectriciansForums.net

LiamC1

DIY
Reaction score
2
I bought my house 11 months ago with no issues, after a few months everything metal in the kitchen starting giving me an electric shock when touched. After a few more months this stopped on its own, and has recently started again. We realised that it only happens when not wearing shoes, if that helps. Any help and advice would be much appreciated. Thankyou.
 
Is it a short sharp 'zap' which may be static, or a longer 'tingle'?

Have you had any work done in the house recently?
 
Wearing shoes or not you shouldn't be getting shocks from metalwork in your house! What are you getting shocks from? Sockets, switches, sink, taps, radiators?
I get a shock whenever I touch my metal socket covers, the sides of the microwave, the toaster, the kettle, the metal front on my oven or any other appliance which I use which is metal. Not from my sink or taps or radiators though.
 
A long tingle for the whole time I touch it, and about 6 months ago I had someone out to fix my lights as all of the lights went in the house but it happened before this too.

You need to get this checked out. Don't leave it another 6 months.

What was causing the lighting problem?
 
I get a shock whenever I touch my metal socket covers, the sides of the microwave, the toaster, the kettle, the metal front on my oven or any other appliance which I use which is metal. Not from my sink or taps or radiators though.
You need to check whether there is an earth path on your sockets. If your earth is faulty, the electrical filter of your washing machine, tumble dryer or maybe your microwave, allows a trickle of electricity through the exposed metalwork of the machines and other appliances, which will give an electric shock.
 
Is it a simple fix?

No way of knowing. Ffs get an electrician in soon . Sorry to be blunt. Proper electrician, not a friend who tinkers with stuff.

Sounds like you may have been without a proper earth for some time. All it takes now is for a live-to-earth fault to happen in an appliance and you may end up dead.
 
Last edited:
Most faults like this, Although they have the potential to be very dangerous (even fatal)

Are often a simple fix if you have the correct knowledge and equipment to test first, diagnose, fix, TEST AGAIN.
it could be as simple as a cable that is not connected, or broken.
a fault with the distributers supply to your house could also be the cause (they will fix that for free same day)

A professional electrician will tell you what the problem is and who/how it can be fixed and made safe.

depending on how your house is wired and plumbed, it MAY BE THE CASE that if you touch one of the items that is giving you a shock AND a radiator/sink etc. AT THE SAME TIME, especially with wet hands. THE SHOCK COULD BE A LOT WORSE. a couple of hundred people die in the uk from similar accidents in the uk each year.
 
No way of knowing. Ffs get an electrician in soon . Sorry to be blunt. Proper electrician, not a friend who tinkers with stuff.

No way of knowing. Ffs get an electrician in soon . Sorry to be blunt. Proper electrician, not a friend who tinkers with stuff.

Sounds like you may have been without a proper earth for some time. All it takes now is for a live-to-earth fault to happen in an appliance and you may end up dead.
Will do.
 
Most faults like this, Although they have the potential to be very dangerous (even fatal)

Are often a simple fix if you have the correct knowledge and equipment to test first, diagnose, fix, TEST AGAIN.
it could be as simple as a cable that is not connected, or broken.
a fault with the distributers supply to your house could also be the cause (they will fix that for free same day)

A professional electrician will tell you what the problem is and who/how it can be fixed and made safe.

depending on how your house is wired and plumbed, it MAY BE THE CASE that if you touch one of the items that is giving you a shock AND a radiator/sink etc. AT THE SAME TIME, especially with wet hands. THE SHOCK COULD BE A LOT WORSE. a couple of hundred people die in the uk from similar accidents in the uk each year.
I have had an electrician out to it but they couldn't see what the problem was as they were obviously wearing boots. Only thing I don't understand is why it happened months ago, and then stopped for a couple of months and has recently started again. What could cause it to stop for a while and then randomly start again..
 
I get a shock whenever I touch my metal socket covers, the sides of the microwave, the toaster, the kettle, the metal front on my oven or any other appliance which I use which is metal. Not from my sink or taps or radiators though.
If it's causing you to worry get an EICR done Electrical Installation Condition Report done. better safe than sorry.
 
I have had an electrician out to it but they couldn't see what the problem was as they were obviously wearing boots. Only thing I don't understand is why it happened months ago, and then stopped for a couple of months and has recently started again. What could cause it to stop for a while and then randomly start again..
What testing did they carry out?
 
I have had an electrician out to it but they couldn't see what the problem was as they were obviously wearing boots. Only thing I don't understand is why it happened months ago, and then stopped for a couple of months and has recently started again. What could cause it to stop for a while and then randomly start again..
As above what testing did they do. Looking for a fault like this you do not intentionally recreate the shock scenario to verify it, you test. The fact it came, went and came back again may well be a lose earthing conductor or cpc.
 
ANY FORUM MEMBERS NEAR STOKE??

please offer this new member a site visit.

It is disappointing to hear that you have had someone look at it and you are still none the wiser.

I would expect anyone coming onto a fault like that to start with a simple earth loop test, it will take a few minutes to plug in a tester and find out if there is a good earth connection to the circuit in question.

the most likely outcome is that there is a fault with the wiring in your house, it is also possible that it is from an external source like a buried cable but that is far less likely.

i do know a good spark that is part P registered and lives over your way.
if you want his details then send me a personal message and i will give you Ian's contact details.
 
Please get a proper spark in. If you ask him if he is 18edition qualified.

as an aside but not giving you any reason for not doing the above :

it could be static electricity where you build up static depending if you are wearing nylon etc. The static is released when you touch a metal surface.

BUT you need to get it checked as a kitchen is not a safe environment if you have an earth fault
 
Went to fit some dimplex heaters the other day. Customer had already had a go fitting two of them. When I touched the casing I could feel some voltage on it. I said as much to the customer, they felt and said "Oh yeh, never noticed that" So took off the spur and even though he had googled it and took photos of the original heaters wiring....That single 6181y is live btw. That was the end of his career in electrics. No surprise there was a live on the casing. So it can happen a number of ways.
 

Attachments

  • IMG_1220.JPG
    84.8 KB · Views: 70

Reply to Keep getting electric shocks in kitchen. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top