Discuss Kitchen 3 gang isolator grid in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
0
Hi guys. I've had my kitchen 're fitted and in doing so 're wired. The hob and cooker both off of 32 ampseperate breakers in 6mm cable.
The rest is on a socket loop 2.5 mm cable in to a 32 amp breaker. But linked into the loop is a 3 gang isolator grid for cooker hood fridge and washing machine. We done this to not have seperate isolators dotted round the room. All the sockets tested fine and sockets spurred off of isololators are testing fine. Trouble is once you plug an appliance in it trips the 2 80amp rcd breakers in garage. Any ideas people?
 
N-E fault. might even be on an unrelated circuit. when you connect a load, some of the current travels down the cpc instead of the N , thus causing RCD/s to see imbalance. a thorough test is advised.

or it could simply be a N conductor is terminated in the wrong bar in CU.
 
Yes, you've probably connected the neutral into the wrong busbar in the consumer unit.

It sounds to me like this is a new circuit. Have you notified the LABC?
 

Reply to Kitchen 3 gang isolator grid in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hi all. So I'm designing my new kitchen and trying to plan where things will go. I currently have a 6 switch panel for the appliances (hob...
Replies
18
Views
1K
DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
Replies
34
Views
3K
Hello Electrical world. Looking for thoughts and opinions. Currently planning out my kitchen re-wire for new kitchen. I was originally...
Replies
13
Views
3K
Bit of advise if anyone has time.. I have a customer who brought a new kitchen from wrens. Customer has had the route to the kitsch redecorated...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock