As someone doing a kitchen refurbishment project for the first time (and now having learnt the hard way why you should never leave your kitchen fitter in charge of sourcing the electrician), I was a bit surprised about the state the electrical works were left in and just figured I'd check here if this is acceptable or breaks some obvious regulations.

In short, where the old wires in the wall were all running through metal conduits, the electrician left the new ones for me to fill in. (see images) It does looks like somewhat bad practice to me, but perhaps not strictly against any regulations, and as long as I get the certificate from the NICEIC and have it verified to guard me against future inspection failures I am kind of ok with patching it up, tiling over and assuming no one will ever try to drill into the kitchen tiles without turning power off at the mains. But I just want to know there's no obvious regulations broken by not having any housing for them?

IMG_20160926_162524.jpg


IMG_20160926_162533.jpg


IMG_20160926_162612.jpg
 
Whilst it's not the neatest work the cables have been run in safe zones and so assuming they are RCD protected then it is fine to plaster over them. They should have capping over them to avoid any damage caused by a plasterers trowel however I don't believe there is a regulation that stipulates that, it's more best practice.

If you don't have an RCD then it would be against the regulations to leave the cables as they are unprotected and less than 50mm deep.
 
Very true Risteard, It's a rather large chase though and so I assumed (perhaps incorrectly) it's running to another accessory. Perhaps the OP could confirm.

The biggest issue is whetehr it is protected by an RCD. If it is not is definitely doesn't comply, if it is then it most likely complies
 
I believe the cable is connected to my cooker, which is turned on via a switch in the cupboard above it. The big hole was my old socket panel which obstructed the kitchen install and is going to be quite a filling job. Still don't know how he managed to drill through the wall into my bathroom, but luckily for both of us it's the next thing on the list of home improvements. :p

So yeah, guess it's as I thought then: not non-compliant, just a bit shoddy. As long as I get the certificate (which is proving to be a challenge) I'll have enough peace of my mind. Will check turning off fuses in the fusebox (that's enough to check if the cables are RCD protected I guess?), but should be fine as well.

IMG_20160929_012449.jpg


IMG_20160929_012611.jpg
 
The electrician is a member of a competent person scheme? You need more than just his certificate. Within a month of completion you should also receive a building control notice stating that the work has been notified and thus is all legal.

Did he install the cooker switch in the cupboard? That is something I'm really not a fan of unless really necessary. In the event of something going wrong you (or whoever is using the cooker at the time) may need to quickly isolate the cooker and so the switch needs to be within easy reach. Edit: it is not against the regulations to install them in cupboards however I prefer not to.

You should see the rcd in the consumer unit, it will have a test button. When you press the test button it should trip all the circuits that it's protecting (it may be all of them, half of them or if it could be an RCBO in which case it will just trip the one circuit). If you're unsure just post an image of your consumer unit here and we can say :)
 
Last edited:
The first picture seems to show a cable running technically just outside of the prescribed zones.
You are absolutely correct, the horizontal chase route should be no wider than the width of the accessory and this is the route the cable should take.
 
There is no regulation regarding capping or oval conduit, yes it is poor practice, it is only to protect the cables from the spreads trail, and of course for rewiring purposes if done correctly.
 
Yeah, I wasn't too fond of having the two switches for the hob/oven in two separate cupboards when I saw that, as having them there does waste space, but seeing as it was already done after I came back from work and the cupboards drilled through I didn't request to have it changed. Didn't think too much of the safety aspect but maybe I should considering the comments here. :)

"I've got a sneaking suspicion that the OP has done this and the phantom electrician does not exist...........just saying."

Oh, I can assure you the "phantom" electrician does exist, But your comment sure shows why I need that electrical installation certificate that my kitchen fitter is currently holding for ransom!

At least the work HAS been notified to building control and I've got a "Building Regulations Certificate of Compliance" from NICEIC by email when I called them, but it is incredibly vague, just saying "Electrical / Install one or more new circuits" in the "Description of Notifiable Work" section. Nothing about the sockets moved, new 32a feed wired externally, wiring hob/oven etc.

He and his company do NOT appear in the search on Home - http://www.electricalcompetentperson.co.uk which does raise yet another alarm bell. But he does appear in the NICEIC local contractors search, as well as in the search on www.competentperson.co.uk. Not sure of why this inconsistency is here...

"Guidance note 1 page 68, 4.7 page 98, 7.5"

What document are you referring to? "Guidance note 1" is a bit too generic to give me the right results on Google...
 
Last edited by a moderator:
Yeah, I wasn't too fond of having the two switches for the hob/oven in two separate cupboards when I saw that, as having them there does waste space, but seeing as it was already done after I came back from work and the cupboards drilled through I didn't request to have it changed. Didn't think too much of the safety aspect but maybe I should considering the comments here. :)

At least the work HAS been notified to building control and I've got a "Building Regulations Certificate of Compliance" from NICEIC by email when I called them, but it is incredibly vague, just saying "Electrical / Install one or more new circuits" in the "Description of Notifiable Work" section. Nothing about the sockets moved, new 32a feed wired externally, wiring hob/oven etc.

He and his company do NOT appear in the search on Home - http://www.electricalcompetentperson.co.uk which does raise yet another alarm bell. But he does appear in the NICEIC local contractors search, as well as in the search on www.competentperson.co.uk. Not sure of why this inconsistency is here...
QUOTE]

.

Installing cooker switches in cupboards, may be acceptable in certain circumstances, i.e. when there is nowhere else suitable to mount them in proximity to the appliance it isolates. However, installing an isolator directly above an appliances is not good practise, for obvious reasons.

The description of the work carried out, on the Building Control Certificate, is I'm afraid going to be just that vague. There are only similar tick boxes on the from to be completed by the installer. What should be more precise, is the extent of the work, which should be described on the Minor Works Certificate, or your case an Electrical Installation Certificate (as the LBC have been informed of new circuits).

You describe having difficulty obtaining the certificate from your installer? Are you in dispute with them, i.e. have you paid for the work yet? Any electrical works requires some form of certificate (within reason!), and the certificate is part & parcel of the work, so having you invoice not paid is not a reason to issue a certificate. Although I have to say, it normally takes me some time to complete a certificate, and my invoice is usually paid before I've issued my cert's ;)

If you are in dispute with your installer, and you feel the work is below standard and the installer is unwilling to rectify, you could contact the NICEIC (if indeed the installer is registered with them). NICEIC will have a mediation process
 
I'm interested in knowing why some feel it's bad practice to not use capping? Surely it's a case of horses for courses, but not using it doesn't necessarily mean bad practice. It's easy enough to stick capping on a wall which hasn't been finished (example breezeblock on a new build), but in a chase of an old terraced house with 107 coats of different plaster and the brick course put in by Stevie Wonder installing capping is usually a lot more trouble than it's worth.

When you want to keep chases narrow and clean, I find that clipping is a lot neater and easier - the cables aren't likely to be damaged by the plasterer in a narrow chase. Granted, you can't say that was a narrow chase in the OPs case but that wall looks like all sorts of hell - to me if you tried to install capping on that it would look like the Ultimate roller coaster at Light Water Valley.

To say not using capping is always bad practice is just wrong in my opinion though.
 
I'm interested in knowing why some feel it's bad practice to not use capping? QUOTE]

You quite right, we all understand the reasoning for using channelling or capping. If it's a very narrow chase the plasterers trowel is unlikely to damage the cables. There was an electricians fable, that the plaster attacked the cable, probably true of lime plaster, but not the stuff used in last few decades. I don't for example use capping in dot & dab walls, but having watched the dry liner slapping on his adhesive, perhaps I should!

I always use capping in chases, and knowing the reasons I don't have to, but choose to do so. The only reason I can give, is that shows a pride in ones work and just taking that little bit more effort. And if the cables do get damaged by what ever means, I have a slim chase of pulling in a new cable.

I'm sure there are other examples of unnecessary practises , but in the OP's case I think the lack of capping perhaps suggests a general standard of poor workmanship, but by just looking at a few pictures, we shouldn't really speculate, which I guess is what your saying.

I would suggest the OP contacts NIC, to see if they are willing to inspect. Or perhaps contacting the installer first?
 
with kitchens, i generally find that it's best to run cables diagonally, all over the place, as kevin kitchen fitter only drills his fixing holes directly above or below the sockets. this way. ot's only random that he hits your cables.:mangry:
 
I have a tonne of capping in the garage, and use it whenever I can. But I'm just thinking of a more recent job where I opened the chase up quite wide to accommodate the capping but it was a nightmare. In the end I opted for clips and it looked much neater than it ever would have looked with capping on it. Would hate for someone to post it on a forum and say "is this right" for it to be ripped to shreds when really there was good cause for not using capping.

I'm not saying this is the case for the OP at all. It looks a mess, but who's to say when he chased the wall the plaster was rubbish and it just fell away - I've had that happen multiple times. Makes your work look shoddy as hell, but there's more to it than what a simple picture portrays.

So yes Midwest, I'm just saying it's wise not to speculate too much.
 
I'm not saying this is the case for the OP at all. It looks a mess, but who's to say when he chased the wall the plaster was rubbish and it just fell away - I've had that happen multiple times. Makes your work look shoddy as hell, but there's more to it than what a simple picture portrays.

So yes Midwest, I'm just saying it's wise not to speculate too much.

Well, to clarify: I did say that "The big hole was my old socket panel which obstructed the kitchen install", so it's not like I 'm claiming he created all of that void just from poor drilling alone, if that is what it's come across like.

I originally posted this as I was curious to know of regulations for conduits, given that the old wiring had it everywhere and I was surprised to see he didn't bother with it at all.

Anyway, given that most people's opinion is that it is a job on-the-edge-of-regulations but not strictly invalid, I'll just leave it be and hope that no future homeowner is careless enough to drill in these areas with power on. And learn to ask the right questions about a planned install beforehand... :)
 
If you used capping or just clipped into the chase in these parts (Northern Ireland) you would be thought to be a cowboy - by the builder and other trades, building control and often the customer. Generally anything chased into walls here is in conduit.
 
I think this all comes down to personal pride in the job, whether or not it is technically correct is irrelevant in my book, all it needed was to be fed in a bit of oval conduit in the correct zone, job done, cost about 10p! I would not be happy leaving anything similar for anyone to see who may come in after me.
 
I think this all comes down to personal pride in the job, whether or not it is technically correct is irrelevant in my book, all it needed was to be fed in a bit of oval conduit in the correct zone, job done, cost about 10p! I would not be happy leaving anything similar for anyone to see who may come in after me.
Couldn't agree more I always use oval conduit up to the box entry and into ceiling cavities so hopefully cables can be withdrawn if necessary. We live in a world of falling standards and fast fix solutions, the gap between new school and old school skills is huge.
 
If you used capping or just clipped into the chase in these parts (Northern Ireland) you would be thought to be a cowboy - by the builder and other trades, building control and often the customer. Generally anything chased into walls here is in conduit.
Undoubtedly true, but we fail to consider the effect on the wall of unnecessarily deep tracks. But as you say if you did it another way you'd be the worst in the world.
 
A little while back, I worked in an old hotel which had been taken over by the Local Authority and was being used as a hostel.
We had to re-wire two floors.
All the cables were in capping and I only found one run where it was not possible to replace the cables down the capping.
 
At risk of copping incoming rounds ... I was raised on conduit in walls (or on em) and so that's what I do. Conduit in the wall helps if the accessory end needs a little bit more, after some clutz mullers it .
 
If you used capping or just clipped into the chase in these parts (Northern Ireland) you would be thought to be a cowboy - by the builder and other trades, building control and often the customer. Generally anything chased into walls here is in conduit.
Just curious, is this in domestic properties and conduit, metal or plastic?
 
I do quite a lot of kitchen fitting, and being multi skilled I do the complete job including first fix electrics & pluming, plastering, tiling and installing the kitchen. In fact I got into this because I was fed up of following other trades and having to deal with one problem after another.

A good tradesman (in my opinion) will consider the whole job. In that he/she will take into account what other items need addressing and how they will be installed.
As an electrician or plumber it is your responsibility to ensure that cables, pipes and accessories are installed with consideration to the customers requirements and also importantly the installation of the kitchen.

I have seen many occasions where a cable run has been installed directly where a kitchen unit is most likely to have the mounting plates installed. The kitchen fitter gets the blame for drilling the cable, when in some cases it is a partial blame situation. Its not rocket science, it takes ten minutes to mark out on the walls where units are likely to be fixed in place. Or failing that get the installer to do it so those areas can be avoided where possible.

My point being, yes its not good practice to just leave the cables un-capped, but capping offers little protection against a drill bit. It is far worse practice to not consider the whole install. Too many folk go in there do their bit and walk away with no concern for the next person to follow.
 
I'm interested in knowing why some feel it's bad practice to not use capping? Surely it's a case of horses for courses, but not using it doesn't necessarily mean bad practice. It's easy enough to stick capping on a wall which hasn't been finished (example breezeblock on a new build), but in a chase of an old terraced house with 107 coats of different plaster and the brick course put in by Stevie Wonder installing capping is usually a lot more trouble than it's worth.

When you want to keep chases narrow and clean, I find that clipping is a lot neater and easier - the cables aren't likely to be damaged by the plasterer in a narrow chase. Granted, you can't say that was a narrow chase in the OPs case but that wall looks like all sorts of hell - to me if you tried to install capping on that it would look like the Ultimate roller coaster at Light Water Valley.

To say not using capping is always bad practice is just wrong in my opinion though.
Hi Hightower. Would have thought oval conduit for a chase would be the best option. Nice and neat any easy to replace cables if needs be in the future.
 
We had a kitchen installed together with an extension that involved a good part of the rest of the house incl. electrics.
We changed from gas to eletric / induction hob and opted to not have those UGLY cooker switches in the kitchen at all. Both hob and cooker are separately fused on whatever was stipulated anyway. So if any work needs to be done I would always switch off the whole circuit at fuse board level anyway rather than just the switch.
 
I worked on one kitchen install, where the designer wanted the sockets and switches precisely posisitioned to allow for the surrounding tiling to line up, so the lines between the tiles would line up with the center of each accessory both horizontally and vertically.
The wall was concrete and we running singles in conduit.
After all the chases were completed, the wall looked like a tube map.
 
I have seen many occasions where a cable run has been installed directly where a kitchen unit is most likely to have the mounting plates installed. The kitchen fitter gets the blame for drilling the cable, when in some cases it is a partial blame situation. Its not rocket science, it takes ten minutes to mark out on the walls where units are likely to be fixed in place. Or failing that get the installer to do it so those areas can be avoided where possible.

QUOTE]

:D

The kitchen fitters I do work for, draw some lovely lines on the walls, where all the wall and floor units are going, so I don't put my drops directly where they need to put their fixings.

Bloody nice blokes :D
 
I was kinda thinking cookers, 3 gang switches etc.
If needed a 2nd conduit drop is used - 3 gang switches 1 drop is generally more than enough as we use PVC/PVC Singles, PVC/PVC Singles & Earth as well as Twin & Earth. Oh and Twin Brown for strappers lol.
 
If needed a 2nd conduit drop is used - 3 gang switches 1 drop is generally more than enough as we use PVC/PVC Singles, PVC/PVC Singles & Earth as well as Twin & Earth. Oh and Twin Brown for strappers lol.
Blimey, almost a different world. When using singles, is that used through the rest of the property, or do you use a combination of singles and tw&e? Wot about larger cables 6&10mm? (see Risteard kinda answered the last).
 

Reply to Kitchen electrical work - are naked cables ok or not? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
979
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
943
Hi, A few years ago I had some cables run from my fuse board to my kitchen. The cables were laid inside my house through the concrete base. There...
Replies
31
Views
4K
Hi there. I’m hoping for some advice. I currently run a small limited company that provides IT services, both commercial and domestic so I...
Replies
0
Views
666
hi i had an EICR report done for a property i let. It had a number of C1 and C2 observations. I got a different electrician to come in and...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock