Discuss LED bulbs Dim glow!!!! in the Australia area at ElectriciansForums.net

N

nosparks100

I went out to a property today and the tenant had 6 down lights connected to a 3 way switch system. The down lights worked great! When the tenant installed LED bulbs there seemed to be a dim glow from the bulbs. The bulbs are 240V 2W. When the switches are off there is 47V at the fittings.
Can anybody help with this one???!!!!!
 
induced voltage due to 2/3 way switching, a snubber might help.
 
This phenomenon is caused by the final circuit cable capacitance. It is more common in conventionally wired two way and intermediate switching circuits due to the wide spread use of 3+E cable and the extra parallel capacitance that creates. LED lamps are particularly sensitive to this because they require very little current to drive the lamp.
The mains LED lamp is essentially a number of LEDs driven by a constant current driver powered by a mains rectifier and smoothing capacitor.
Even though the live feed to the LED lamp is switched OFF the cable capacitance allows leakage current to flow to the lamp slowly charging the smoothing capacitor in the lamp until the potential is sufficient for the constant current driver to "fire" the LEDs. This discharges the smoothing capacitor, the constant current driver stops, the LEDs extinguish and the process of charging starts again ... if conditions are suitable this continues indefinitely.
If the charge/discharge cycle (repetition rate) is short, the LEDs appear to be 'ON' continuously, however the energy is limited so the LEDs are only barely lit.
If more lamps are added to the final circuit the loading on the cable capacitance can be such that the individual smoothing capacitors of some or all of the lamps do not reach "firing" potential. Or you may find that only one or a few lamps on a circuit are effected due to the distribution of the cable capacitance and the manufacturing tolerances of the lamps. This can be quite disconcerting the first time you encounter it.
A tungsten filament lamp doesn't suffer this problem because the filament is permanently loading the cable capacitance and any acquired charge is unable to overcome the thermal inertia.
A simple solution is to permanently discharge the cable capacitance by wiring two 160K ohm, 1/4W, resistors rated at >=250V, in series across L and N on the final circuit, it is good electronics practice to do this as close to the effected lamp as possible, if this is done across the switched L and N at the lamp holder terminals it allows simple switching out of circuit (or disconnection) for testing. Do not try to use a single 330K ohm resistor because this may fail due to voltage breakdown.
If the final circuit has a large number of switched lamps it may be pragmatic to connect the series resistors between permanent L and N at a convenient point e.g. at the DB to reduce the number of resistors required, however the number of points that will require treatment will depend on how the cable capacitance is distributed on the final circuit. Additional points particularly where 3+E is used for 2 way and intermediate switching may well require additional pairs of resistors.
If this solution is implemented a notice should be placed at the DB stating which final circuits are effected and how they have been modified.
 
Last edited by a moderator:
Thanks for that. Some really good technical advice. What would I do if there is 6 effected down lights that are dimly glowing? (on the same 3 way switch) Sorry if that sounds thick!
 
I had this problem on a kitchen lighting circuit.
i fitted a 400v 0.1uf capcitor across the switchline and neutral at the light fitting problem solved for me.
worth a go £2.87 from maplins.
 
I had this problem on a kitchen lighting circuit.
i fitted a 400v 0.1uf capcitor across the switchline and neutral at the light fitting problem solved for me.
worth a go £2.87 from maplins.

Ouch! 2x160k Ohm, 0.6W, resistors 26p each from Maplin, cheaper 1/4W types available elsewhere.
 
Thanks for that. Some really good technical advice. What would I do if there is 6 effected down lights that are dimly glowing? (on the same 3 way switch) Sorry if that sounds thick!

The solution is cheap enough that you can afford to do all 6 lamps if necessary, but normally you'll have to do less than half of them. Do a lamp at a time, functional test after each modification, until the problem disappears. I would choose the last lamp on the final circuit, then if required a lamp near the middle of the circuit and if required then the first lamp on the circuit, etc. Usually I find one pair of resistors is all that is required.
 
Last edited by a moderator:
a snubber is, afaik, a combination resistor/capacitor which is wired L/N or SL/N, as said above, trial and error as to where and how many you have to fit.
 
merloy99, in the UK a 3 way switch is a 2 way???? EH 3 way switching is not 2 way. Im not american at all. 3 way switching includes an intermediate switch.
Your phrasing is a new one on me mate!
 

Reply to LED bulbs Dim glow!!!! in the Australia area at ElectriciansForums.net

Similar Threads

Good Morning, I've used this forum for advice many times but this is my first time posting so I hope that this community can help! We're...
Replies
5
Views
1K
Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
197
Evening guys! I have three of these bulbs on a ceiling light, controlled by a dimmer switch installed by an electrician...
Replies
8
Views
2K
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
Driven by the recent colossal hikes in the cost of electricity I hit upon the wizard wheeze of replacing some of the existing LED bulbs in our own...
Replies
2
Views
930

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock