Not to blame Andy! Not sure what you mean by switch wire rather than neutral. Both the roses and the switch only had a single red (live) and black (neutral) plus earth, which is not like any other circuit in the house. So how the rest of the circuit is wired I do not know. It was put in about 30odd years ago and I was working in those days so didn't see it installed.
 
Not to blame Andy! Not sure what you mean by switch wire rather than neutral. Both the roses and the switch only had a single red (live) and black (neutral) plus earth, which is not like any other circuit in the house. So how the rest of the circuit is wired I do not know. It was put in about 30odd years ago and I was working in those days so didn't see it installed.

If you only have 2 cores at the switch, one must be live and the other must be a switch wire, very often in a 3 plate lighting circuit (see pic), a twin and earth cable run to the switch is used like this with the red core being the live feed to the switch and black core used as the switch wire. If you have the same at the ceiling rose and the red has become the switch wire and the black is the neutral... It looks like there may be junction boxes somewhere...

View attachment 35966
 
Thanks Andy - there could well be junction boxes elsewhere. Like I say I didn't see any of it go in. Furthermore the builder went bust in the middle of the job, which meant that a number of things were not as expected!
 

Reply to LED Bulbs won't work together on same circuit. in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Good Morning, I've used this forum for advice many times but this is my first time posting so I hope that this community can help! We're...
Replies
5
Views
1K
Driven by the recent colossal hikes in the cost of electricity I hit upon the wizard wheeze of replacing some of the existing LED bulbs in our own...
Replies
2
Views
942
Hi all. I'm new to this forum so thank you for having me. I'm having an issue with my bathroom lights. I have x4 MR11 3.5mm Spots. They've been...
Replies
17
Views
2K
I really need help with this puzzler. First - I am moderately 'skilled' in day-to-day basic wiring. My puzzle: I am trying to replace a...
Replies
10
Views
1K
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
708

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock