Discuss LED flood straight off ring?? C2 or C3?? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
19
Carrying out a EICR. Stumbled on 2 x portacabins. Testing the ring in bottom portacab to find an SY 2.5mm has been spurred off the dado sockets, exits the bottom cab clipped externally upto the top of the top cab and supplies an LED flood. Automatically i thought its wrong. No spur. But im now thinking C3. Its a fixed load. It supplies 1 x light on the top of a high level portacabin. What are peoples thoughts? Obviously Zs commplying. The DB is inside the cab for local isolation.
 
Carrying out a EICR. Stumbled on 2 x portacabins. Testing the ring in bottom portacab to find an SY 2.5mm has been spurred off the dado sockets, exits the bottom cab clipped externally upto the top of the top cab and supplies an LED flood. Automatically i thought its wrong. No spur. But im now thinking C3. Its a fixed load. It supplies 1 x light on the top of a high level portacabin. What are peoples thoughts? Obviously Zs commplying. The DB is inside the cab for local isolation.
The fuse is to protect the cable. If its a fixed load theres no chance of overload to the cable. The ocpd in db will supply fault protection. Additional RCD too.
it is your judgment to say c2 or c3 you the one that signs the test certs .
 
The fuse is to protect the cable. If its a fixed load theres no chance of overload to the cable. The ocpd in db will supply fault protection. Additional RCD too.
th
c2 or c3.
 
There are probably millions of non compliant spurs connected from ring final circuits which are never going to create a hazard. You must consider has this part of the circuit been correctly designed, no. Is the led light a fixed electrical load, no. Is the choice of SY cable the correct choice in respect to external influences, no. Is it acceptable to connect a multistranded conductor into the socket terminals with other conductors which are solid core??, no.
You decide.
 
There are probably millions of non compliant spurs connected from ring final circuits which are never going to create a hazard. You must consider has this part of the circuit been correctly designed, no. Is the led light a fixed electrical load, no. Is the choice of SY cable the correct choice in respect to external influences, no. Is it acceptable to connect a multistranded conductor into the socket terminals with other conductors which are solid core??, no.
You decide.
fair enough,badpractice, but can you justify a C2 as a potential danger?
 

Reply to LED flood straight off ring?? C2 or C3?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good afternoon all, today I experienced a near death electric shock. This happened on a single phase domestic property! I was carrying out a few...
Replies
15
Views
3K
Hi all, Planning on wiring my neighbour's summer house which will be 15 metres away from the end of the house (20-25 metres total distance from...
Replies
29
Views
7K
Ok, I'm back with another question for your consideration. Quick recap, we are refurbishing a building for the Men's Shed charity. It's a single...
Replies
4
Views
2K
A
Hi guys I’m new to this site however just thought I’d give my best explanation of what the AM2 was like. If this is in the wrong forum I’m very...
Replies
29
Views
12K
G
Two twin sockets spured off ring main in a 2.5mm t+e. just straight from ring no 13a fused spur. I know you can have one twin socket. Would you C2...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock