Search the forum,

Discuss LED Lamps and extractor fan problems.. in the UK Electrical Forum area at ElectriciansForums.net

A

ash_s3

A friend of mine has just replaced some halogen GU10 lamps in his bathroom with LED lamps from Amazon.

Hes saying since swapping the lamps, the extractor fan runs continuously. (230v in-line unit in the loft with over run timer)

He tried swapping one LED lamp back to halogen and it worked as it should, timing out after 5mins or so.

Removed the halogen (with the lights switched off) and the fan fired up by itself!

Anyone come across this before? Sounds like a resistance issue to me, would a resistor sort this out?

Cheers
 
Hi,

Sounds like something is wired wrong or badly connected as the fan switching is nothing to do with that of the actual lamp holder or the load connected to it IMHO.
 
Yes I see what your saying, I was thinking of some kind of capacitance in the lamps themselves? Once switched off, still holding a small charge.
I could be talking nonsense but just wanted to see if anyone else had any clues before I go take a look! Thanks
 
You've got a small amount of capacitive or inductive coupling from a permanent live to the switched live powering the lights (and fan trigger).

With at least one halogen lamp fitted, its relatively low resistance is enough to reduce the phantom voltage to a negligibly low value, so the fan switches off as normal. If you only have LED lamps fitted, they will have a fairly high impedance non-resistive loading on the switched line, which will allow the phantom voltage to rise to sufficient level to trigger the fan. Adding a well chosen resistor across the switched line and neutral will sort the problem. A low wattage filament lamp would do (as you have found) although a much higher resistance will do the job. The resistance value required will have to be found by experiment and the resistor wattage chosen to suit.

Alternatively, some re-routing of the cables may do the job. May require separating the switched live from the permanent live.
 
Last edited:
Thank you, so the voltage could be inducing inside the 3C+E to the fan?
Similar sort of problem to the dimly glowing LEDs on 2way switches then.
 
We have had same issue with central extract systems çonstantly boosting due to some sort of issue with a small voltage at switched live. This is interesting.
 
If the fan is coming on when switch is off, then the fan is wired incorrectly...nothing to do with lighting.

The fan has been working fine for 18months with halogen lamps in the bathroom, can't be wired incorrectly in my opinion mate.
 
Hi, another solution if the circumstances suit it, would be to wire a 3core+e to the switch then change the switch to a DP one, giving each "switched live" it's own pole which are electrically separated when the switch is off.
 
Hi, another solution if the circumstances suit it, would be to wire a 3core+e to the switch then change the switch to a DP one, giving each "switched live" it's own pole which are electrically separated when the switch is off.


Not ideal with an over run timer!
 
Hi, what I mean't was, one switched live to the lights, one to the fan, which would of course still have it's permanent live.
So the fan no longer picks up it's switched live from the lights but is connected through to it's own pole of the switch.
 
Look at this...

fanwiring3_h2.jpg
 
+1 for capacitive coupling.

If it all works fine with gu10s then misbehaves with LEDs fitted then I don't see how it can be connected incorrectly.

How much voltage are we talking about here?

Also, when you say it turns the fan on, if it was only a capacitive thing, then surely it will run out this making the fan switch off on the end of its timer run?
 
How much voltage are we talking about here?

Also, when you say it turns the fan on, if it was only a capacitive thing, then surely it will run out this making the fan switch off on the end of its timer run?

We're not talking about DC filling up a cap which then triggers the fan. The capacitive coupling is AC, providing a weak link between the perm live and switched live; it's a continuous process, so 'running out' doesn't come into it.

No idea of the voltages involved. The voltage required to trigger the fan and the input impedance will vary from one model to the next.
 
Just saying really, didn't have any comment on it, just for the lesser educated on how its connected thats all, more information than anything.


This is how I see it.
The permanent live is always at the fan, this permanent live is inducing a voltage in the switched live of the 3c&e, the LED lamps won't illuminate with such small voltage so the voltage stays in the conductor.
With halogens, the voltage is dropped through the filament?
i take it that with these timer fans, the motor runs off the perm live and the switched live is just a trigger to start the timer? So even a small voltage could trigger it?
 
Then the SWL and L to the fan must be wired incorrectly with the lighting circuit.....by removing the halogens which you state brings on the fan, whilst switch off. I would Ask where is the fan getting the SWL voltage from..?
 
I'm sticking with the theory of its wired incorrectly. I don't buy the inductance thing, we are talking about a bathroom light not a supermarket full of lights.

It's been poorly wired and incorrectly too and we have not been told the full picture like I've frigged around with it and don't know what I'm doing....
 
Not experienced this myself, but if it is wired correctly, you could install a relay next to the fan or the isolator to disconnect the SL from the lamps when the switch is off.
 
How much voltage are we talking about here?

Also, when you say it turns the fan on, if it was only a capacitive thing, then surely it will run out this making the fan switch off on the end of its timer run?

How can capacitive coupling run out?

If the trigger for the fan is over sensitive then it could take next to nothing to trigger it.
 
I'm sticking with the theory of its wired incorrectly. I don't buy the inductance thing, we are talking about a bathroom light not a supermarket full of lights.

It's been poorly wired and incorrectly too and we have not been told the full picture like I've frigged around with it and don't know what I'm doing....

You're mixing inductance and capacitance up, they are two different things.

Capacitive coupling is the effect which caused CFLs to flash and LEDs to glow/flash when installed on some 2 way switched circuits.

In what way are you suggesting it has been wired incorrectly? Can you describe the wiring method you think will cause this bizarre behaviour? I am curious as I cannot think of any way of connecting this which will cause he behaviour described.
 
I can't think what it could be but I bet your bottom dollar that there's more to this than is made out.

If you can't come up with a way of connecting this that will cause the problem then why state that the problem is with the way if is connected ?

Random speculation doesn't help anyone.
 
It's wired correctly as I installed it about 18 months ago.
Hager J804 in the loft, feed in, twin to pull cord, twin to spotlights and a 3c&e to TP fan isolator then onto the fan.
Fan is a Manrose MF100T, wiring hasn't been interfered with in the meantime.
 
It's wired correctly as I installed it about 18 months ago.
Hager J804 in the loft, feed in, twin to pull cord, twin to spotlights and a 3c&e to TP fan isolator then onto the fan.
Fan is a Manrose MF100T, wiring hasn't been interfered with in the meantime.

Wire it with the Line and S/L on the outer cores, N in the middle.
 
Archy- You think it's picking up the voltage for the contacts inside the isolator?

Sorry, a bit vague there, I mean the cable.
May as well do the same at the isolator.

If it isn't already wired this way, give it a try and let us know the result...put us all out of our misery! :smilielol5:
 
Sorry chaps I'm not really following here.

Connecting the Line and S-Line opposite ends of the isolator - is this to keep the cores apart in the pattress?
 
Sorry chaps I'm not really following here.

Connecting the Line and S-Line opposite ends of the isolator - is this to keep the cores apart in the pattress?

In the cable!

Do you understand how capacitive coupling works?
There are many threads on here discussing if if you search.
 
Ah I see now, so the N and E are in between the two Lines of the cable.

And no I'm not clued up on capacitive coupling, just youtube'd it and nearly slipped into a coma listening to the guy!
 
Then read up on it and understand it before you go any further.

Then you can diagnose whether or not this is the problem and design a suitable soloution.
 
I'm using the term in its general sense, "Bring about or give rise to". What's the concise term for "to cause a current to flow due to capacitive coupling"?

When discussing electricity the word induce has a specific meaning, using it otherwise is only going to give rise to confusion.

I doubt there is a concise term, we are talking about a technical/scientific subject which is something that doesn't work well with shortening terms down for convenience
 
I'm using the term in its general sense, "Bring about or give rise to". What's the concise term for "to cause a current to flow due to capacitive coupling"?

I think in these cases, it's just a case of the circuit acting as a capacitor connected across an AC voltage source.
So it's just the 'natural' (high end terminology there!!!) current flow, in these cases in the order of micro Amps.
Which are starting to have a/or producing, odd effects on newer low power gear.
 
This may, or maynot be helpful but....

Today I investigated a bathroom where the lights (LED's) stayed on when the lights were off!

So I removed the cover of the ceiling mounted fan...... and narrowly avoided being "drenched" by the build up of water (condensation) that had accumulated and clearly the moisture was providing the "connection" between the SL and L.

With the fan cover off, and the fan disconnected, the lights now work perfectly.

Hope this is of use to some of you!W Court Fan.jpg
 

Reply to LED Lamps and extractor fan problems.. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, my niece lives in a flat and has a bathroom without a window. There is an extractor fan which packed up and an electrician installed a new one...
Replies
4
Views
813
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
778
Good afternoon everyone. I have fitted an extractor fan in my bathroom with an overrun timer, to start when the bathroom led lights are turned on...
Replies
92
Views
9K
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
609
Hi. I’ve got two pendant lights that currently run halogen lamps. One of the converters is broken so I’m planning to change both for LED lamps...
Replies
1
Views
641

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top