Discuss LED lights in communal area strobing in the UK Electrical Forum area at ElectriciansForums.net

SparkyAndGeorge

-
Esteemed
Arms
Reaction score
235
Hi all,
Been called out to communal lights in a flat communal area. 3 out of the 9 LED lights are strobing roughly once a second. When the timelag switches are pressed the strobing stops and the lights illuminate as they should but when the timelag switch pops back out the strobing starts again. I measured the voltage and am getting
S/L - N = 60v/120v fluctuating
S/L - E = 60v/120v fluctuating
P/L - N = 230v
N - E = 0v
Any suggestions please? Many Thanks
 
put one only incandesant light on the circuit,
this usually fix's it.
must be incandesant, cannot be led or cfl.
The easiest way is to swap out one of the led bulbs.
Same fixture just put a small incandesant in there.
 

Reply to LED lights in communal area strobing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
747
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
287
I had just installed a heat alarm on the downstairs lighting circuit during a kitchen rewire. The new kitchen ring / cooker circuit I tested IR...
Replies
4
Views
4K
I have a issue with lights flickering in my home. Specifically led lights. I’ve bought a lot of brands of led lights and even most of the...
Replies
0
Views
2K
Just spent 4 hours tracing out a lighting circuit to try and find a fault. I came across a switch that was switching the neutral. This threw me...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock