Just spent 4 hours tracing out a lighting circuit to try and find a fault.
I came across a switch that was switching the neutral. This threw me as I was getting 230V on the S/L (to earth) at the light when I switched the light off!!! I then realised the Neutral was being switched, which I haven't come across before.
Also have 0.02Mohms N-E (same circuit as above) which I've partially tracked down to mixture of 1 or 2 junction boxes hidden under floorboards, between 3 sets of lights.
All switches and lights were poorly wired (jumble of cables forced in, insulation breaking down, back boxes loose, filled with plaster and other mess).
I could tidy up the switches, spend 1/2 day taking up carpet and floorboards and perhaps find a single junction that solves all the problems. Or, I could spend 1/2 day taking up carpet and floorboards and get absolutely nowhere and then rewire anyway!
I'm erring towards a rewire of the 3 lights at switches in question. 2 x living room and 1 x landing.
What would you guys do?. Continue fault finding or partial re-wire of lighting circuit?
I came across a switch that was switching the neutral. This threw me as I was getting 230V on the S/L (to earth) at the light when I switched the light off!!! I then realised the Neutral was being switched, which I haven't come across before.
Also have 0.02Mohms N-E (same circuit as above) which I've partially tracked down to mixture of 1 or 2 junction boxes hidden under floorboards, between 3 sets of lights.
All switches and lights were poorly wired (jumble of cables forced in, insulation breaking down, back boxes loose, filled with plaster and other mess).
I could tidy up the switches, spend 1/2 day taking up carpet and floorboards and perhaps find a single junction that solves all the problems. Or, I could spend 1/2 day taking up carpet and floorboards and get absolutely nowhere and then rewire anyway!
I'm erring towards a rewire of the 3 lights at switches in question. 2 x living room and 1 x landing.
What would you guys do?. Continue fault finding or partial re-wire of lighting circuit?