Discuss Fault find or rewire? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
Just spent 4 hours tracing out a lighting circuit to try and find a fault.

I came across a switch that was switching the neutral. This threw me as I was getting 230V on the S/L (to earth) at the light when I switched the light off!!! I then realised the Neutral was being switched, which I haven't come across before.

Also have 0.02Mohms N-E (same circuit as above) which I've partially tracked down to mixture of 1 or 2 junction boxes hidden under floorboards, between 3 sets of lights.

All switches and lights were poorly wired (jumble of cables forced in, insulation breaking down, back boxes loose, filled with plaster and other mess).

I could tidy up the switches, spend 1/2 day taking up carpet and floorboards and perhaps find a single junction that solves all the problems. Or, I could spend 1/2 day taking up carpet and floorboards and get absolutely nowhere and then rewire anyway!

I'm erring towards a rewire of the 3 lights at switches in question. 2 x living room and 1 x landing.

What would you guys do?. Continue fault finding or partial re-wire of lighting circuit?
 
I lean towards rewire, dependant on ease of isolation from the rest of the circuit.
Out of interest, what are the cable colours (old or new)?
 
I lean towards rewire, dependant on ease of isolation from the rest of the circuit.
Out of interest, what are the cable colours (old or new)?
old red and black - metric.
 
Rewire it everytime. Just had a job, no cpc on one half of a flat. Could have gone in the double lofts looking for the fault. Could have taken ages as there were two lofts, insulation and carpet and boarding of a sort move it all and maybe just maybe find the fault. So I just bridged two lighting points with t&e used just the earth and hey presto problem solved in half an hour.
 
Last edited:
When that happens I just tell the customer that I always seek to act in their best interests and it's better for both them and I to undertake a job of known length to remove many problems than to spend even more indeterminate time trying to find the damaged cable.
(You may be able to IR the switch wires and re-use them)

Funnily enough this video I've just watched seems strangely relevant....the usual language disclaimer applies, but it's a great example of logic going completely out the window when testing and searching for a needle in a haystack.
 
This is one of those jobs where a good cable tracer is worth it's weight had one a little while ago where the customer had put the floorboards down during a rewire the circuit in question started to trip the RCD occassionally the cable tracer identified the offending nail it was only a short length of cable so I just rewired it

I could tidy up the switches, spend 1/2 day taking up carpet and floorboards and perhaps find a single junction that solves all the problems. Or, I could spend 1/2 day taking up carpet and floorboards and get absolutely nowhere and then rewire anyway!

I'm erring towards a rewire of the 3 lights at switches in question. 2 x living room and 1 x landing.
Not quite understanding why you need to lift floorboards to locate the fault but to rewire you don't, if you lift the floorboards to locate the fault and subsequently need to rewire or partially rewire then you already have some of the work done for rewiring
 

Reply to Fault find or rewire? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
Replies
10
Views
889
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
856
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
671
Hi, in my bedroom i had a 2 gang dimmer that powered 2 set of 3 spot lights and also had passthrough wires to other sockets. Im changing to just...
Replies
2
Views
257
My wife has a electric heated airer, our dog chewed through the cable and I thought it would be no different from rewiring a plug. It's not. I...
Replies
2
Views
786

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock