Hi all,

Hoping someone can help with the below and excuse my novices!!!!

I have 8 Parathom LED spot 111 50 advanced lamps wired in series, they are each 8.5w and are replacing existing halogens. I am struggling to find a driver that is able to run them all and have spoken to Osram who were no help at all. I have found the varilight YT150Z (Premium Electronic Lighting Transformer 0w - 150w - https://www.tlc-direct.co.uk/Products/LTYT150.html) would this be suitable or can someone please recommend something that would be suitable please?

Many thanks and apologies if this is a very stupid question.

Martin
 
had a look on the Osram site, those seem be running off 12V AC.
Why you wired them in series??? That will complicate things a lot, you will need some 50-80volts to run whole lot.
If done in parallel configuration a standard 230-12v transformer rated above 68 watts (8 lamps rated 8.5 watts each = 68 watts) should do the job.
 
those power supplies are NOT 12vdc output, they are a pulsating 12v
sort of in between DC and AC.
as the Parathom data sheet does NOT specify DC only
I can only guess that they will work But you will NOT get full life from them
If long term reliability is important ?
Then use a 12vdc regulated power supply.
specialist electronic suppliers will have them.
 
those power supplies are NOT 12vdc output, they are a pulsating 12v
sort of in between DC and AC.
as the Parathom data sheet does NOT specify DC only
I can only guess that they will work But you will NOT get full life from them
If long term reliability is important ?
Then use a 12vdc regulated power supply.
specialist electronic suppliers will have them.

Manufacturers datasheet says 12V with operating frequency 50-60Hz.
Looks more or less AC to me.
 

Reply to LED Problem, help please!!! in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
So often we have these difficulties...incompatible LEDs/dimmers...lamps staying lit, dimly and dimmers not doing the job. I hope to assist a...
Replies
15
Views
2K
Hi, I have a hob extractor with 2x halogen MR16 / GU5.3 light bulbs. The transformer inside it is this one...
Replies
9
Views
15K
Hi, I was hoping someone could help me. I have recently brought a 3rd gen nest and installed it myself. I am currently using the usb stand however...
Replies
12
Views
7K
S
Hello, I wonder if someone can help me here. My understanding is : Leading edge dimmers are suitable for mains GU10 halogen lamps, but need to...
Replies
9
Views
1K
scanner
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock