Length of meter tails

Discuss Length of meter tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
55
Been asked to quote a job - total rewire of four flats. As individual flats it's all very straight forward, ring, lighting, shower etc. However UK Power networks are installing a new head and meters for the whole block on the ground floor.

Obviously the distance to the top flat is going to be at least 10 metres. In terms of bringing up the meter tails do I have to put in an isolator every 3m or what?
 
Only one fused switch per set of tails ( Isolator is not a protection device) at the origin if the installation is all that is required

Now depending on your cable choice, method of erection and earthing system, these factors will determine what protection device you can use
 
Cor blimey guvnor, strike a bleedin lite I thinks its a fused switch at the origin or I'll be a Marry Poppins...oi you, take a look at my "william" 12inches folded in half!!! ahhhhhhhh
 
There is no regulation, well not in the BS 7671-2008 at least.

The 3-5 metre length is normally a DNO requirement. The OSG does advise this in section 2.2.3, but there is no actual length advised, just to contact the DNO
 

Reply to Length of meter tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top