Search the forum,

Discuss Less sensitive smoke alarms in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Guitarist

-
Esteemed
Reaction score
2,744
I went to price a job up today and noticed the lady had physically disconnected her 2 interlinked smoke alarms, due to them always going off.
Obviously, I was concerned to see this and pointed out that not only is this dangerous, but that her insurance is probably invalid. She is a heavy smoker, which obviously doesn't help, but she claims that even steam from the bathroom will set them off!
I didn't get to see what make they were, but they were installed when the house was built 8 years ago.
I am keen to get 2 new ones installed that she can live with and would like any suggestions from you guys please. I like the look of the Aico Ei166RC, but have no experience of this model.
 
Last edited:
Were they actually going off or were they "bleeping"? If its the later maybe they need a good hoovering. I can't imagine that cigarette smoke alone would set them off unless she's a continual chain smoker.
 
As above, try cleaning the chamber. Maybe they can be replaced with rate of rise heat detectors as opposed to smokes. I'm guessing this is domestic given the alarm and smoking environment.
 
Were they actually going off or were they "bleeping"? If its the later maybe they need a good hoovering. I can't imagine that cigarette smoke alone would set them off unless she's a continual chain smoker.

She said that they were "going off" on a regular basis, whenever she cooked, had a shower, and no doubt lit-up. It is a small 3-up, 2-down place so not a lot of circulation space.
There is the possibility that one of the originals was faulty from new, and she just took them out without bothering to check. If I was to install a new pair of good optical alarms, at least we would have done our best to minimise the amount they go off. It may be that she smokes around the house the originals were just too sensitive.
 
Sorry to jump in on thread......
To comply with part B of building regs it says mains interlinked fire alarms to be fitted on new builds plus refurbished houses. What exactly does it mean by refurbished.....is it just relating to a rewire ?
 
Last edited:
they sound like they are probably old ionisation detectors replace them for some new optical or if your worried about false alarms dual sensor units the ones you mention should be ok
the old ones are near the end of there life as they should be changed every 10 years
and steam or even hair spray and deodorant can cause an alarm due to the partical size
and an odd false alarm when the place fills with steam or burns the toast is a good thing because they will never test it anyway
 
Would bet that the ones fitted were ionisation alarms. Contractors fit ions to new build because they are cheaper than optical alarms, despite the fact opticals are recommended for escape routes.

The smokes are probably contaminated and causing false alarms.

You should fit opticals - which the Aico 166s are.

Heat alarms should never be fitted to escape routes
(with the exception of dual sensor alarms). They detect the heat from a fire - by which time you won't be able to escape that way!!!
 
I went to price a job up today and noticed the lady had physically disconnected her 2 interlinked smoke alarms, due to them always going off.
Obviously, I was concerned to see this and pointed out that not only is this dangerous, but that her insurance is probably invalid. She is a heavy smoker, which obviously doesn't help, but she claims that even steam from the bathroom will set them off!
I didn't get to see what make they were, but they were installed when the house was built 8 years ago.
I am keen to get 2 new ones installed that she can live with and would like any suggestions from you guys please. I like the look of the Aico Ei166RC, but have no experience of this model.

Wrong type of detectors used.

in Incorrect locations.

Change the detector type

Change the detector location.

and install a Hush/test button.
 
I went to price a job up today and noticed the lady had physically disconnected her 2 interlinked smoke alarms, due to them always going off.
Obviously, I was concerned to see this and pointed out that not only is this dangerous, but that her insurance is probably invalid. She is a heavy smoker, which obviously doesn't help, but she claims that even steam from the bathroom will set them off!
I didn't get to see what make they were, but they were installed when the house was built 8 years ago.
I am keen to get 2 new ones installed that she can live with and would like any suggestions from you guys please. I like the look of the Aico Ei166RC, but have no experience of this model.

Aico are good. But how long since she disconnected them? Six or seven years? Have they never been satisfactory?
 
Guitarist I think your on the right lines with your thinking, as others have said the aico does seem to be the best to fit and I would give it another vote, Its all I fit now.
You say the existing were fitted eight years ago so most start to get a over sensitive after 5 years or so, I think may normally be due to dust build up and most people never clean them. A bit like the tv screen they attract dust inside and i guess the components overheat a bit.
I tend to advise they run the hoover hose round them now and again to keep it down, I get the mrs to do this at home to the ones I fitted 10 yrs ago (aico) and had no problems yet. In saying that the ones before them we used as a dinner gong but the wifes cooking is much better now.
 
Probably all that tar and nicotine building up in them has knackered them. I'd hate to see the state of my lungs... :lol:
 
I tend to advise they run the hoover hose round them now and again to keep it down, I get the mrs to do this at home to the ones I fitted 10 yrs ago (aico) and had no problems yet. In saying that the ones before them we used as a dinner gong but the wifes cooking is much better now.

That'll be as per the Manufacturers instructions then !!
 
Thanks for all the replies. I should have asked exactly when she took them down, but as I said, I was there looking at another job at the time and didn't have very long.
I think I will quote her for fitting 2 new Aico Ei166RC and give her some advice on keeping them clean.
Moses, relocation not really possible as the ceilings are really small and I think the original sparky got them pretty spot-on. Thanks for the input tho :)
 
Even if you fit new optical alarms right near a bathroom, if there's loads of steam then they'' still probably go off.

Every manufacturer advises of siting anywhere near a bathroom.
 
Extension just done, one Aico fitted. Now Building Control say they want 2 more in the house, can you fit wireless ones. Told him 'Yes, but she'll have to turn her radio on for them to operate'. For about 10 seconds he actually looked worried.lol.
 
Extension just done, one Aico fitted. Now Building Control say they want 2 more in the house, can you fit wireless ones. Told him 'Yes, but she'll have to turn her radio on for them to operate'. For about 10 seconds he actually looked worried.lol.

3 alarms just because of an extension? Thought you only needed that with new-builds.
 
If the extension is substantial and of course depending on the type, i have been required to install smoke alarms to all floors.

I use the Aico, and if you can get a feed to it, you can use the radio bases for linking duties.

They also do a remote wireless switch that can be used in many configurations.
 
3 alarms just because of an extension? Thought you only needed that with new-builds.

Disabled grant job for local authority. He wants one in the new extension and two in the house, one at the foot of the stairs and one on the landing, all interlinked.
 
Thanks for all the replies. I should have asked exactly when she took them down, but as I said, I was there looking at another job at the time and didn't have very long.
I think I will quote her for fitting 2 new Aico Ei166RC and give her some advice on keeping them clean.
Moses, relocation not really possible as the ceilings are really small and I think the original sparky got them pretty spot-on. Thanks for the input tho :)

If you have the interlink wired then EI146 Optical smoke alarms might be cheaper than EI166RC.
 
You might want to suggest CO and heat alarms (for any gas boiler and kitchen) as well.
I nearly suggested something else to the awkward sod.
Not a bad idea though, top. Trouble is the budgets. They allow for as little as possible at the design stage and expect the tradesmen to bend over backwards. It's about priorities, so safety should be at the top of the list. The all singing, all dancing bog costs more to buy than my full job. (it's bloody good though, not that I've tried it).
 
If the extension is substantial and of course depending on the type, i have been required to install smoke alarms to all floors.

I use the Aico, and if you can get a feed to it, you can use the radio bases for linking duties.

They also do a remote wireless switch that can be used in many configurations.

Yeah, cheers Jason. It's only bedroom, utility and walk in shower. Got a mains supply to the one in the extension so just need a radio base to link with the other two. Doubt I'll get an extra for it though.
 
If you have the interlink wired then EI146 Optical smoke alarms might be cheaper than EI166RC.

Thanks for the suggestion. They are a little cheaper, but use alkaline batteries. I think that if I am going to put my name to this, I will quote for the units with a 10 year battery life :)
 
3 alarms just because of an extension? Thought you only needed that with new-builds.
I think alot will depend on the existing house layout and differences from council to council as they work from a list of advise and regulations and I'm sure we have all had cases where they hear something that sounds good and tell you they want it as if it was regulation.
Round my way if an extension that includes a bedroom is off a lounge or kitchen meaning the fire exit route from the bedroom passes through these rooms the need for additional smokes is required to cover both sides of the route so have become the norm for me.
I guess this is due to the information they work from advises kitchens and lounges being the two most likely souces of fire, well it was when they let me see their notes he quoted from.
 

Reply to Less sensitive smoke alarms in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
370
I don't fit alarms as my main job but have fitted quite a few over the years whilst we were doing the electrics side of things. I usually fit the...
Replies
0
Views
166
Not come across this before, so would like some help, please. I went to install smokes and heat alarm (to new Scottish regs) in a fairly modern...
Replies
2
Views
1K
I am an electrical labourer currently doing my own research on Alarms to self-educate as much as I can. I would like to state the general rules I...
Replies
15
Views
2K
I installed some aico smoke detectors about a year ago. They are interlinked with radio bases. The customer has just discovered that when she...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock