J

jimma22

Hello all, has anyone come across lighting and sockets on same feed, basically a house has been extended, and from the CU it goes out in 2.5mm2 and in the loft it looks like junction boxes have been used to feed the lights in 1.5mm2 instead of laying on a separate feed for lighting. How rough is this.
 
i would say that as long as the maximum load on the 1.5 cable doesnt go above its current carrying capacity, then its ok. Its definately not the way i would install it, but technically theres nothing wrong with it from a bs7671 point of view, apart from maybe division of circuits to avoid inconvenience
 
the crux of my point above, is that overload protection is not required iof a load is fixed. A lighting load will be fixed. always assume the worst case regarding lamp sizes though, ie 100W pendants, 50W GU10's
 
Don't think any of us are shocked anymore by what we find sometimes, just when you think you have seen the worst job ever another corker rears its head. If nothing else it keeps us all talking in the wholesalers.
 
Looking at it today though it looks like the ring main is feeding 5 lights in total. i would of thought at the time of the extension it would of been easier to put a separate feed for the lights in anyway.
 

Reply to Lighting and Sockets on same feed in House extension in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
906
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
704
Hi, I’m new to the forum. Thanks for letting me join. Asking for some diy advicd… I’m trying to add a couple more security lights to the existing...
Replies
1
Views
708
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
819
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
426

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top