shocksmith222

Hi All,

I am a newbie to the forum so please be gentle! :eek:

Today I have come across a recently rewired house and I noticed that the installing sparky has indicated on the Install Certificate that the lighting circuit is T&E 2 core 1.5mm and CPC 1.5mm. However, I have noticed that in fact there appears to be several runs where T&E 2 core 1.5mm and CPC 1.0mm has been used instead.

From a testing point of view it is fine and Max Zs is well within the Regs guidelines. I am just wondering 2 things and despite checking my regs cant find any 100% answer.

1. For the certificate - should it actually have been issued stating the smaller T&E 2 core 1.5mm and CPC 1.0mm rather than as it is now T&E 2 core 1.5mm and CPC 1.5mm?

2a) Am I obliged to advise the client that the T&E 2 core 1.5mm and CPC 1.0mm should now be replaced with the same cable as used in the majority of the lighting circuit, that is T&E 2 core 1.5mm and CPC 1.5mm
OR
2b) Can I simply leave it as it is and just advise the client that there is a mix of CPC size on the lighting circuit. Afterall the safety disconnect of the circuit is fine anyway.

Thanks to all in advance for your views.
 
Hi All,

I am a newbie to the forum so please be gentle! :eek:

Today I have come across a recently rewired house and I noticed that the installing sparky has indicated on the Install Certificate that the lighting circuit is T&E 2 core 1.5mm and CPC 1.5mm. However, I have noticed that in fact there appears to be several runs where T&E 2 core 1.5mm and CPC 1.0mm has been used instead.



From a testing point of view it is fine and Max Zs is well within the Regs guidelines. I am just wondering 2 things and despite checking my regs cant find any 100% answer.

1. For the certificate - should it actually have been issued stating the smaller T&E 2 core 1.5mm and CPC 1.0mm rather than as it is now T&E 2 core 1.5mm and CPC 1.5mm?

2a) Am I obliged to advise the client that the T&E 2 core 1.5mm and CPC 1.0mm should now be replaced with the same cable as used in the majority of the lighting circuit, that is T&E 2 core 1.5mm and CPC 1.5mm
OR
2b) Can I simply leave it as it is and just advise the client that there is a mix of CPC size on the lighting circuit. Afterall the safety disconnect of the circuit is fine anyway.

Thanks to all in advance for your views.

I didn't know that you could get 1.5mm T&E with a 1.5mm cpc I thought all 1.5mm T&E had a 1mm cpc.
 
As pennywise said, record the smallest value. it's quite common to see mixed conductor sizes. One common practice was to wire the circuit in 1.5 and use 1.0 f or the switch drops.
 
Hi - I've got the same issue at the moment: I'm, doing a pvc conduit installation using 1.5mm single core cpc on the lighting circuits in conduit (no supplier could get me 1mm single core), however there are places where I am going over to 1.5mm/1mm twin & earth outside conduit, where it seems sensible to do so.:) Is this OK?
(First post! - whew)
 
Hi - I've got the same issue at the moment: I'm, doing a pvc conduit installation using 1.5mm single core cpc on the lighting circuits in conduit (no supplier could get me 1mm single core), however there are places where I am going over to 1.5mm/1mm twin & earth outside conduit, where it seems sensible to do so.:) Is this OK?
(First post! - whew)

It's fine! Just record the smallest CSA on the cert, and you could also note the differing sizes too. If Zs are OK then what's the issue?
 

Reply to Lighting Circuit - Mixed CPC Sizes! in the Australia area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
803
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829
Hi, So I've just started to install some spotlights in a room in my house, and I always thought to use 1.5mm T&E so I've wired them all up and...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock