Hi Gents,

Just a quick question. I'm adding some lights to an extension, just a few spots which I plan to take from the existing downstairs lighting circuit using a junction box.
Question being, do I need to add an FCU?
I'm comparing this this adding a spur to a ring final circuit and if adding more than one socket, you'd add a FCU.
Does the same rule apply to lighting circuits? There's going to be about 9 spotlights and two outside lights.
Has RCD protection etc
Thanks
T
 
if you are taking the feed from a lighting circuit, no need to add a FCU as it's already on a 5A/6A fuse/MCB. just ensure that allconnections are compliant and safe. test circuit after alterations.
 
I'm comparing this this adding a spur to a ring final circuit and if adding more than one socket, you'd add a FCU.
The point is that the requirement for an FCU applies to adding more than one socket to a RING FINAL circuit.
Lighting circuits are RADIAL circuits where there is no restriction on the number of devices/accessories on a circuit subject to (but not restricted to):
  • cabling distance
  • the value of the protective device on the circuit and (of course)
  • the total demand.
 

Reply to Lighting Circuit Spur Q&A in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
648
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
696
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
739
Hi all, I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock