Hello.
I have a possible issue with the lighting circuits in my house.
There are two lighting CCTs:

Dropbox - 01.JPG - https://www.dropbox.com/s/ike2aygjja64pfm/01.JPG?dl=0

1 LIGHTS supplies:
Lounge
Kitchen
Downstairs toilet

2 LIGHTS spplies:
Hall
Upstairs landing
Upstairs bedroom
Upstairs spare room
Upstairs bathroom

In the hall, there is a doble switch, one controlling the upstairs landing light, and the other controlling the hall light.

Dropbox - 02.JPG - https://www.dropbox.com/s/3cech5ldpcaj8ky/02.JPG?dl=0

here's where I'm confused, but there's nothing new there.

With 1 LIGHTS CB tripped, and 2 LIGHTS CB still on, all lighting on 1 LIGHTS can still be powered on by operating the downstairs LANDING light switch.

and...

With 2 LIGHTS CB tripped, and 1 LIGHTS CB still on, the upstairs landing light can be operated with the downstairs landing light switch.

and...

upstairs landing, bedroom, spare room and bathroom lights can be operated with the downstairs or upstairs landing light switch.

I am not convinced that this is normal, even though my wife assures me that the "electrician" who did the installation some years ago said it was all above board and legal.

Any input on the matter?

Thanks,
Gary
 
Hello.
I have a possible issue with the lighting circuits in my house.
There are two lighting CCTs:

Dropbox - 01.JPG - https://www.dropbox.com/s/ike2aygjja64pfm/01.JPG?dl=0

1 LIGHTS supplies:
Lounge
Kitchen
Downstairs toilet

2 LIGHTS spplies:
Hall
Upstairs landing
Upstairs bedroom
Upstairs spare room
Upstairs bathroom

In the hall, there is a doble switch, one controlling the upstairs landing light, and the other controlling the hall light.

Dropbox - 02.JPG - https://www.dropbox.com/s/3cech5ldpcaj8ky/02.JPG?dl=0

here's where I'm confused, but there's nothing new there.

With 1 LIGHTS CB tripped, and 2 LIGHTS CB still on, all lighting on 1 LIGHTS can still be powered on by operating the downstairs LANDING light switch.

and...

With 2 LIGHTS CB tripped, and 1 LIGHTS CB still on, the upstairs landing light can be operated with the downstairs landing light switch.

and...

upstairs landing, bedroom, spare room and bathroom lights can be operated with the downstairs or upstairs landing light switch.

I am not convinced that this is normal, even though my wife assures me that the "electrician" who did the installation some years ago said it was all above board and legal.

Any input on the matter?

Thanks,
Gary
Whereabouts in the UK are you situated?
 
Am in Peterborough.
I’m not sure how long it’s been like this, I only discovered it recently by chance when I changed a lightswitch like for like. And yes I got the wires in the correct holes :)
 
Are you saying with either circuit breaker off, not both all lights still function.
 
Am in Peterborough.
I’m not sure how long it’s been like this, I only discovered it recently by chance when I changed a lightswitch like for like. And yes I got the wires in the correct holes :)
Post Code?
 
But the landing switches need to be in a certain switching position for this to happen?
 
They are interconnected then possibly at the switches.
 
shared neutrals????.
 
There is no tripping issue, as neither CB’s have tripped at all.
It’s only when either one CB is off and the other is on.
So Westward wins the toaster
Will keep you updated...
 
so do i win the kettle?
 
There is no tripping issue, as neither CB’s have tripped at all.
It’s only when either one CB is off and the other is on.
So Westward wins the toaster
Will keep you updated...
Gary haveyou read my PM of an offer to come and take a look at your problem? if you don't want any help please at least let me know.
 
There is no tripping issue, as neither CB’s have tripped at all.
It’s only when either one CB is off and the other is on.
So Westward wins the toaster
Will keep you updated...
Gary haveyou read my PM of an offer to come and take a look at your problem? if you don't want any help please at least let me know.
Whereabouts in the UK are you situated?
It was part of an offer to help, jim_e_ jib so why the dumb post?
 

Reply to Lighting circuits and possible cross-over in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
520
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
880
Hi everyone, I really hope someone will be able to help. So last night I tried to change 2 ceiling rose / pendant lights at my mother in laws...
Replies
5
Views
1K
Hi folks, Quick query for this still practicing regarding bill payment for a job not complete. My partner recently employed an electrician to do...
Replies
11
Views
1K
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock