Discuss lighting in the metal shed in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi,

Need a word of advice, how should I run supply to two metal sheds that are located about 20m away from the main DB. Should I run in SWA with 10mm bonding and as separate circuit to each shed or through sub-board adjacent to them? What IPX of switch and lighting should be, I'm expecting some condensation as the sheds seems sealed?
Thanks
Mike
 
I believe you can have the SWA connected to the home earthing arrangements, in this case TNCS. At the shed consumer unit when terminating the SWA use a plastic compression gland only. This will then separate the SWA earthing from the shed earthing arrangements. As the shed is of metal construction TT earthing will be required.
 
I'm thinking of sub-DB that split into two 6A lighting circuits, 4mm2 cable. Earthing arangement is TNCS so ideally 10mm bond but have no experience with this, so I can TT with RCD protection.
 
If 4mm is your calculated cable, run this as a normal circuit from your internal dist board. However when terminated into you new dist board you will need to seperate the earth and all paths back to the PME system. Then install a earth rod and TT the new installation. Dont forget to use the correct RCD protection for tmyour circuits, and if neccessary bond the metallic sheds.
 

Reply to lighting in the metal shed in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Hi, I'm running a 70ft underground UF cable in 3/4 inch PVC conduit to 2 sheds. The sheds are 3ft from each other. I'm just a DIYer enthusiast so...
Replies
1
Views
750
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
528
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
615

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock