Discuss Lighting MCB keeps tripping in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
28
Hi all.

Just after a bit of advice.

Just got home on Christmas Eve, went to put the lights on as you do, then there was a "pop" from the MCB.

Usually when this happens one of the halogen bulbs in the bathroom has gone and needs replacing. Usually resetting the MCB, identifying the blown bulb and replacing does this trick.

This time, the MCB trips straight away. Won't reset at all.

We've been through the house, checked all lights are off. Still won't reset.

We did find an old filament bulb that had gone, so we've taken that out and replaced it, but still the MCB won't reset.

Anyone have any ideas we could try?

The rest of the MCB is fine, we have power to sockets, cooker, etc. Just the lighting affected.

Trying to call local electricians at this time on Christmas Eve isn't going too well.
 
Thanks for the repliess so far, I don't know if it makes any difference, but a little bit more info...

The bathroom has 4x individual GU10 halogen bulb downlighters across the ceiling.
The kitchen has 3x GU10 bulbs in a single ceiling unit.

The rest of the house has energy saving bulbs.

All light switches are set to off, but MCB trips straight away with a "pop".

if it is the MCB damaged, which seems logical, I'll wait until an electrician wakes up on Boxing Day.

Thanks for your quick replies.
 
Hi all.

Just after a bit of advice.

Just got home on Christmas Eve, went to put the lights on as you do, then there was a "pop" from the MCB.

Usually when this happens one of the halogen bulbs in the bathroom has gone and needs replacing. Usually resetting the MCB, identifying the blown bulb and replacing does this trick.

This time, the MCB trips straight away. Won't reset at all.

We've been through the house, checked all lights are off. Still won't reset.

We did find an old filament bulb that had gone, so we've taken that out and replaced it, but still the MCB won't reset.

Anyone have any ideas we could try?

The rest of the MCB is fine, we have power to sockets, cooker, etc. Just the lighting affected.

Trying to call local electricians at this time on Christmas Eve isn't going too well.
Switch all the lighting switches to the off position, reset the MCB and gradually switch the lights back on until the MCB trips, if it does there is your problem circuit.
 
As the MCB is tripping it means you have a short circuit somewhere.

You mention GU10 fittings, I would probably start looking at those fittings for signs of overheating, not the first time a GU10 has been covered in insulation and has melted the wiring PVC.
 
Replying to a few questions in one here...

All lights switches are in the off position. When reset the MCB trips with a pop straight away.

I've just replaced all 4x GU10s in the bathroom with new ones and the same thing happens. (They are operated by a rocker switch outside of the bathroom).

We don't have any outside lights.

I've taken out and left out thr 4x GU10s in the bathroom. Reset the MCB - it doesn't trip this time, but there are no lights in any of the rooms still.
 
I've taken out and left out thr 4x GU10s in the bathroom. Reset the MCB - it doesn't trip this time, but there are no lights in any of the rooms still.
If I've understood correctly you now have the light mcb staying on? But no lights in the bathroom. What happens if you turn on any light switches (even the bathroom light switch) ?
 
If I've understood correctly you now have the light mcb staying on? But no lights in the bathroom. What happens if you turn on any light switches (even the bathroom light switch) ?


Absolutely nothing. mCB is in on position, but no lights in any room

Just noticed there is a tiny little red/green indicator on the MCB.

With all of the others in the ON position the indicator is red.

Now the lighting MCB is in on position, the indicator is green/white
.
 
Apologies if it isn't very clear, just point and hoping for the best ...

IMG-20181224-193348421.jpg
 

Reply to Lighting MCB keeps tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
My kitchen has track lighting. It consists of three halogen light bulbs. I've had the fixture for more than 25 years with no issues. Last night...
Replies
10
Views
936
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock