Discuss Lightning, spds and rcds in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

mhar

-
Esteemed
Arms
Reaction score
414
Went to a property today where the lady is having problems with a 30mA rcd tripping during lightning. This is an upfront rcd protecting a small db in a large metal roofed garage which feeds 1)garage sockets, 2)garage lights, 3)electric gates and 4) fish pond equipment. It is the gates being disabled when the rcd trips that is the problem as she is in her 60's, recently widowed and past her gate jumping days.
I only had access to the garage where she left me installation certs mainly dated 2008 which showed a tt system with a Ze of 48 Ohms on one and 62 on another. On one of the certs it stated that this rcd had been removed but reinstated by the person doing the work. The house has had an extension 3-5 years ago and I assume the earthing was converted to pme as my Zrcd was .37Ohms, I was not left a cert covering this work. Obviously I have further investigations to do next week but it appears that the problem has been around for quite a few years and the earthing system is probably not relevant, the cpc had also been disconnected in the rcd enclosure. The rcd ramps at 21-24mA
I have been thinking along the lines of inserting an spd (Wilts controlgear SS40) between the rcd and the db to protect the rcd from what I assume to be large voltage spikes. My other options being replacing the t&e gate feed with swa so I could have an unprotected feed but this would allow spikes to pass to the house cu, or use four rcbo's and hope that the spikes are not originating from the gate circuit (which is a bit hit and miss for me).
I would be interested in how others have approached similar situations. App 18 of bgb shows spds on the load side of an rcd as I am thinking, I have never dealt with one before. My question is basically about the suitability of this spd, it's likely effectiveness and any other considerations there may be.
Have to go out shortly so there may be a delay in replying.
 
my initial thoughts would be to feed the gates with SWA, fed from a non-RCD MCB as long as that part of the installation is not TT earthing.
 
Is this RCD in the garage? If so split the load with rcbos, so the fish pump and others are separate from the gates. Is the metal work of the garage bonded to the supply?
Any IR issues?
Is the supply now PME or TN-S or TT?
 
Thank you. That was my option no 2. However my concern was that any voltage spikes would then have a path into the main cu. I suppose SWA terminated into an ip rcd at the gates would stop this and the rcd would be accessible to her from outside the gates. Am I overly concerned about these spikes?
 
Remove up front RCD, MCB for gates, RCBO's for the other circuits.
agreed, but he'll need to replace the T/E to the gates with SWA unless it's run in earthed metal conduit.
 
Thanks for the replies.
My concern is that if I do not have any type of rcd or spd (the current rcd is acting as a surge protector) then any spikes will travel to the main cu and trip any rcd there leaving us worse off than now. She will be stuck outside her gates whilst her freezer is defrosting!
I have never used an spd before, the one I referenced is £30 and looks like a solution that ticks all my boxes.
 
Thanks for the replies.
My concern is that if I do not have any type of rcd or spd (the current rcd is acting as a surge protector) then any spikes will travel to the main cu and trip any rcd there leaving us worse off than now. She will be stuck outside her gates whilst her freezer is defrosting!
I have never used an spd before, the one I referenced is £30 and looks like a solution that ticks all my boxes.

why is the RCD required?
 
Went to a property today where the lady is having problems with a 30mA rcd tripping during lightning. This is an upfront rcd protecting a small db in a large metal roofed garage which feeds 1)garage sockets, 2)garage lights, 3)electric gates and 4) fish pond equipment. It is the gates being disabled when the rcd trips that is the problem as she is in her 60's, recently widowed and past her gate jumping days.
I only had access to the garage where she left me installation certs mainly dated 2008 which showed a tt system with a Ze of 48 Ohms on one and 62 on another. On one of the certs it stated that this rcd had been removed but reinstated by the person doing the work. The house has had an extension 3-5 years ago and I assume the earthing was converted to pme as my Zrcd was .37Ohms, I was not left a cert covering this work. Obviously I have further investigations to do next week but it appears that the problem has been around for quite a few years and the earthing system is probably not relevant, the cpc had also been disconnected in the rcd enclosure. The rcd ramps at 21-24mA
I have been thinking along the lines of inserting an spd (Wilts controlgear SS40) between the rcd and the db to protect the rcd from what I assume to be large voltage spikes. My other options being replacing the t&e gate feed with swa so I could have an unprotected feed but this would allow spikes to pass to the house cu, or use four rcbo's and hope that the spikes are not originating from the gate circuit (which is a bit hit and miss for me).
I would be interested in how others have approached similar situations. App 18 of bgb shows spds on the load side of an rcd as I am thinking, I have never dealt with one before. My question is basically about the suitability of this spd, it's likely effectiveness and any other considerations there may be.
Have to go out shortly so there may be a delay in replying.

Thanks for the replies.
My concern is that if I do not have any type of rcd or spd (the current rcd is acting as a surge protector) then any spikes will travel to the main cu and trip any rcd there leaving us worse off than now. She will be stuck outside her gates whilst her freezer is defrosting!
I have never used an spd before, the one I referenced is £30 and looks like a solution that ticks all my boxes.

Before jumping to conclusions you need to take a step back trying to provide a solution without fully investigating the problem seems to be your problem here. I would suggest you approach this with a open mind and not be taken in by what the homeowner is telling you.
First off you need access to all of the installation and not just the garage, I don't know how many lightning storms you get in your location but this could just be a red herring, does this RCD tripping occur at at different times or the same / similar time of day, have you checked what leakage current is present on the CU the fish pond and electric gates from past experience can cause intermittent problems this is what I would be looking at, is there a fridge or freezer in the garage and has the auto defrost heater failed, is it water (heavy rain) getting into outdoor enclosures or underground joints. This is not an exhaustive list but a starting point to provoke some thought

Quite a bit to look at before you spend £30 and possibly not fix the problem
 

Reply to Lightning, spds and rcds in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
891
Hi all, So I’ve been having a strange fault in my house which has just appeared over the past few days. About a month ago I moved my pc set up...
Replies
136
Views
14K
Evening all. I have a question as I can’t get my head around something with solar PV I’m going to be working on a new build in a couple of...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock