Discuss Lights 15 amp circuit dims when hot tub motor kicks, 60amp circuit? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I have an extra 200 amp panel in aux garage and only exterior lights and hot tub are on it right now. Everything my hot tub motor kicks on, the 15amp light circuit with lights dims for a second. The tub is on a 60amp circuit. How can this happen? I thought the purpose of separate circuits is to avoid this.
 
I have an extra 200 amp panel in aux garage and only exterior lights and hot tub are on it right now. Everything my hot tub motor kicks on, the 15amp light circuit with lights dims for a second. The tub is on a 60amp circuit. How can this happen? I thought the purpose of separate circuits is to avoid this.
Everytime the tub motor kicks, not everything
 
Well somewhere you have some common impedance that is allowing the voltage in the aux garage to drop when the load is applied. Motors have a high start-up current which makes them the most common reason.

However, if it really is a 200A capable panel there is no excuse as the tub can't be taking a sizeable chunk of that much. Usually the reason is the supplying cable is not thick enough for the length even if it meets the current carying capacity ('ampicity' I think is the USA expression), but more worryingly it can be down to a bad connection and that presents a fire hazard due to it heating up.

I see you are down as USA location, so maybe one of the American members such as @Megawatt will be along with a bit more country specific advice.
 
Well somewhere you have some common impedance that is allowing the voltage in the aux garage to drop when the load is applied. Motors have a high start-up current which makes them the most common reason.

However, if it really is a 200A capable panel there is no excuse as the tub can't be taking a sizeable chunk of that much. Usually the reason is the supplying cable is not thick enough for the length even if it meets the current carying capacity ('ampicity' I think is the USA expression), but more worryingly it can be down to a bad connection and that presents a fire hazard due to it heating up.

I see you are down as USA location, so maybe one of the American members such as @Megawatt will be along with a bit more country specific
 
I have an extra 200 amp panel in aux garage and only exterior lights and hot tub are on it right now. Everything my hot tub motor kicks on, the 15amp light circuit with lights dims for a second. The tub is on a 60amp circuit. How can this happen? I thought the purpose of separate circuits is to avoid this.
It could be that the main cables feeding your house are a little on the small side.
Its fairly common for high amperage inductive loads to cause a momentary dip in lighting. It doesn't take much difference in voltage to affect lighting.
 
Voltages could be low at the panels which would cause lights to dim when a heavy inductive load starts. Motors need a bit more of a kick to get them going and draw a lot of current when starting, this current has to come from somewhere.
 
I have an extra 200 amp panel in aux garage and only exterior lights and hot tub are on it right now. Everything my hot tub motor kicks on, the 15amp light circuit with lights dims for a second. The tub is on a 60amp circuit. How can this happen? I thought the purpose of separate circuits is to avoid this.
Even though you have a 200 amp panel, what size breaker is feeding it. All hot tubs I’ve wired was on a GFCI breaker which you didn’t mention. Not only the motor pulls a high current on the start up which has been mentioned above the heating elements also pull a high current. If your lights are dimming then it sounds like you don’t have big enough wire feeding the panel
 

Reply to Lights 15 amp circuit dims when hot tub motor kicks, 60amp circuit? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Summary (TL;DR) Several lightbulbs in my home supplied by one circuit breaker dim over time and go out in about a year. Right now, the ceiling...
Replies
0
Views
731
I am a very knowledgeable DIYer with no issues on any beginner to intermediate wiring because my father is a retired electrician. The issue: I...
Replies
10
Views
1K
I am the homeowner of a hot tub that's been working for well for 6 years. One day the water began to provide a shocking sensation which would...
Replies
37
Views
6K
Having lost my father in law many years ago, an electrician and electrical engineer, I'm now at a loss for a sounding board for any issue that...
Replies
1
Views
1K
Hi! DIY electrical guy here. I am hoping someone can point me in some direction on this. I live in Ohio if that helps. We bought this house a...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock