Discuss Lights not on RCD side of board in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hopefully a picture is attached.

The lights in this house are not on the RCD side of the board, there is a spare way which they could slot into and be protected by the rcd.

The lights are not split up and down so no problem between a borrowed neutral between top and bottom tripping the RCD.

Just wondered what other reasons there were why these would not have been put on the RCD side of the board ?

20190407_113342.jpg
 
Lights were routinely placed on the non RCD side of the board in the past, this was probably due to the fact that when lightbulbs blew they tended to take out the RCD, in a one RCD board this would have taken out the whole installation. As this is an old board this is probably the case.
 
Got to disagree with roly I'm afraid, blowing lamps don't take out the RCD, they take out an MCB, usually a type B MCB because of a current surge. The reason lights were not put on the RCD when that board was installed (16th edition) was that it was not a requirement, the RCD side generally only protected socket outlets. This was the accepted practice.
 
Got to disagree with roly I'm afraid, blowing lamps don't take out the RCD, they take out an MCB, usually a type B MCB because of a current surge. The reason lights were not put on the RCD when that board was installed (16th edition) was that it was not a requirement, the RCD side generally only protected socket outlets. This was the accepted practice.
Usually they don't take out the RCD, but it's not guaranteed. I have had an RCD trip due to a blowing lamp before in my own house. Not sure what came into contact with what causing the imbalance.

But I would agree that it is likely to be a 16th Edition installation where providing RCD protection to lighting circuits was unheard of.
 
i'd be even more concerned that it's a protecrap board.
 
I'd be even even more concerned that the CU has been installed on an angle. The electricity is going to pool on the non RCD side.
 
Got to disagree with roly I'm afraid, blowing lamps don't take out the RCD, they take out an MCB, usually a type B MCB because of a current surge. The reason lights were not put on the RCD when that board was installed (16th edition) was that it was not a requirement, the RCD side generally only protected socket outlets. This was the accepted practice.
Must just be my customers then, lamp pops, takes out the mcb which then in turn takes out the RCD. Customer then phones electrician as they have reset the mcb and the electric hasn't come back on......?
 

Reply to Lights not on RCD side of board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
343
I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
821
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock