I've taken the supply from a neighbouring light [power source = outdoor lights] and this now controls the old and new switch as follows:
  • When I turn on the new lights the outdoor lights come on with a low glow
  • When the new lights are turned on and I turn on the outdoor lights, this turns the new lights off, why?

  • The brown cable from the power source goes to L2 = live,
  • the blue cable from the power source goes links to the blue cable cable going to the lights.


This is the wiring diagram I used for the fitting of the intermediate switching

1667137610864.png
 
TL;DR
lights, supply, switch
I've taken the supply from a neighbouring light [power source = outdoor lights] and this now controls the old and new switch as follows:
  • When I turn on the new lights the outdoor lights come on with a low glow
This would suggest that you have the lights connected in series
  • When the new lights are turned on and I turn on the outdoor lights, this turns the new lights off, why?
This suggests that turning on the outside lights is removing the live feed from the new light
  • The brown cable from the power source goes to L2 = live,
  • the blue cable from the power source goes links to the blue cable cable going to the lights.
How have you verified this
This is the wiring diagram I used for the fitting of the intermediate switching

View attachment 103170
What does the intermediate switching control, the diagram you have posted looks to show the blue cable at the light with a brown sleeve

Can you post a diagram of what you have actually done with some pictures of what you have connected where
 
This would suggest that you have the lights connected in series

This suggests that turning on the outside lights is removing the live feed from the new light

How have you verified this

What does the intermediate switching control, the diagram you have posted looks to show the blue cable at the light with a brown sleeve

Can you post a diagram of what you have actually done with some pictures of what you have connected where
Thanks for your quick reply, I'll do my best to answer:

  1. Yes, they're not meant to be, which leads me to think that the supply which comes from the neighbouring switch is taking part in the circuit somehow. I don't know how to prevent that given the drawings, which btw i think show how to take from the consumer unit. I'm not, but I am using a one way switch in the same 4gang switch.
  2. Yes, I would agree, and goes the shared agreement that the source is somehow involved in the loop, though it's not meant to be...
  3. Trying the different light switches, if that's what you meant?
  4. The intermediate switch works correctly as do the other lights in the 3 way system. The brown sleeving is a hangover from the original diagram taken from here https://www.youtube.com/c/GSHElectrical and doesn't act as a switching line or at least that's not my intention
  5. The pictures are difficult to intepret because its a 4 gang switch and its difficult to tell precisely whats doing what. However the diagrams I'm happy to supply. Though again I'm thinking that its easier if I just tell you. It's 2 way switch in a 4 gang plate which is wired to the com and L1 terminals. I've fed the live from the com and the 'neutral' from L1. The 'neutral' from source is connected to the 2 core lighting cable and doesn't connect to the new switch terminals. The live feeds into L2 in the new switch.

    OK I've worked on one image to get you a close up of the neighbouring switch and new 3 way switch.

    Things to note are:
  6. the 'live' is a single wire because I've used a wago to split the live into two - 1 feeding the new switch and 1 feeding the existing one way light. This makes no impact on the outcome other than making it easier to connect up.
  7. The blue cable connects to the lighting blue cable

    1667145223891.png
 
This would suggest that you have the lights connected in series

This suggests that turning on the outside lights is removing the live feed from the new light

How have you verified this

What does the intermediate switching control, the diagram you have posted looks to show the blue cable at the light with a brown sleeve

Can you post a diagram of what you have actually done with some pictures of what you have connected where

I'm thinking I have two options:
  1. Bite the bullet and get a feed from the consumer unit.

  2. Only use the 'live' feed from the neighbouring light, but I don't know if this is safe, nor if it would work, nor what to do with the 'neutral' that is meant to be feeding the light - i guess this would have to connect to the switch - no idea which terminal
 
I'm thinking I have two options:
  1. Bite the bullet and get a feed from the consumer unit.

  2. Only use the 'live' feed from the neighbouring light, but I don't know if this is safe, nor if it would work, nor what to do with the 'neutral' that is meant to be feeding the light - i guess this would have to connect to the switch - no idea which terminal
Actually you do have 4 options

The two you posted

Or do what I suggested in post #2

Or the response most DIYers don't like which is get a spark in to sort the problem out
 
Last edited:
Thanks for your quick reply, I'll do my best to answer:

  1. Yes, they're not meant to be, which leads me to think that the supply which comes from the neighbouring switch is taking part in the circuit somehow. I don't know how to prevent that given the drawings, which btw i think show how to take from the consumer unit. I'm not, but I am using a one way switch in the same 4gang switch.
  2. Yes, I would agree, and goes the shared agreement that the source is somehow involved in the loop, though it's not meant to be...
  3. Trying the different light switches, if that's what you meant?
  4. The intermediate switch works correctly as do the other lights in the 3 way system. The brown sleeving is a hangover from the original diagram taken from here https://www.youtube.com/c/GSHElectrical and doesn't act as a switching line or at least that's not my intention
  5. The pictures are difficult to intepret because its a 4 gang switch and its difficult to tell precisely whats doing what. However the diagrams I'm happy to supply. Though again I'm thinking that its easier if I just tell you. It's 2 way switch in a 4 gang plate which is wired to the com and L1 terminals. I've fed the live from the com and the 'neutral' from L1. The 'neutral' from source is connected to the 2 core lighting cable and doesn't connect to the new switch terminals. The live feeds into L2 in the new switch.

    OK I've worked on one image to get you a close up of the neighbouring switch and new 3 way switch.

    Things to note are:
  6. the 'live' is a single wire because I've used a wago to split the live into two - 1 feeding the new switch and 1 feeding the existing one way light. This makes no impact on the outcome other than making it easier to connect up.
  7. The blue cable connects to the lighting blue cable
    View attachment 103172
If my understanding of what you have done is correct the blue wire needs to be connected to a neutral, where it is currently connected gets a neutral through the light that is fed by the red wire which is why they work dimly and when the switch is on your new lights have 2 lives feeding them and no neutral, quite a simple fix you just need a neutral to connect to you may be lucky and have a looped neutral feed in the switch back box
 
If my understanding of what you have done is correct the blue wire needs to be connected to a neutral, where it is currently connected gets a neutral through the light that is fed by the red wire which is why they work dimly and when the switch is on your new lights have 2 lives feeding them and no neutral, quite a simple fix you just need a neutral to connect to you may be lucky and have a looped neutral feed in the switch back box

"...you may be lucky and have a looped neutral feed in the switch back box"

Sorry, but I don't undertand this... I'm guessing you could mean I might have another neutral I can take from another switch?
 
Actually you do have 4 options

The two you posted

Or do what I suggested in post #2

Or the response most DIYers don't like which is get a spark in to sort the problem out

Reluctant to try my single cable com feed because the neutral bothers me, as in the original diagram clearly shows using the neutral. Although I have seen instances of where people use a single com feed from neighbouring light. The neutral from the light needs to go somewhere.

Post#2 - discuss more, I think I follow but want to be clear what you meant by that.

Pro's - I've tried to get a sparky in but I had quotes of £1000 for the works in three parts including hallway, kitchen, and conservatory. This was after I had one chap offer £250 for the day.
 
"...you may be lucky and have a looped neutral feed in the switch back box"

Sorry, but I don't undertand this... I'm guessing you could mean I might have another neutral I can take from another switch?
Apologies for jumping in - maybe a bit of context might help.
In older properties/ traditional wiring, you do not normally have neutral wires at light switches, all wires are live or swiched live one way or another. The neutral is taken directly to the light fitting only.

More recent installations may take neutral via the light switch position (ie looped through), because with the advent of smart switches, some require a neutral to work, so it's become more commonplace to make that provision for the future.

I suspect you may need to bring in a neutral connection - meaning from that lighting circuit - not any old neutral!

PS you say "The neutral from the light needs to go somewhere." That is the crux of the matter. I doubt you have a neutral at the switch. Just because there's a blue wire doesn't mean it's actually a neutral! If you have a test meter you can check.
 
  • Like
Reactions: UNG
Thanks for your quick reply, I'll do my best to answer:

  1. Yes, they're not meant to be, which leads me to think that the supply which comes from the neighbouring switch is taking part in the circuit somehow. I don't know how to prevent that given the drawings, which btw i think show how to take from the consumer unit. I'm not, but I am using a one way switch in the same 4gang switch.
  2. Yes, I would agree, and goes the shared agreement that the source is somehow involved in the loop, though it's not meant to be...
  3. Trying the different light switches, if that's what you meant?
  4. The intermediate switch works correctly as do the other lights in the 3 way system. The brown sleeving is a hangover from the original diagram taken from here https://www.youtube.com/c/GSHElectrical and doesn't act as a switching line or at least that's not my intention
  5. The pictures are difficult to intepret because its a 4 gang switch and its difficult to tell precisely whats doing what. However the diagrams I'm happy to supply. Though again I'm thinking that its easier if I just tell you. It's 2 way switch in a 4 gang plate which is wired to the com and L1 terminals. I've fed the live from the com and the 'neutral' from L1. The 'neutral' from source is connected to the 2 core lighting cable and doesn't connect to the new switch terminals. The live feeds into L2 in the new switch.

    OK I've worked on one image to get you a close up of the neighbouring switch and new 3 way switch.

    Things to note are:
  6. the 'live' is a single wire because I've used a wago to split the live into two - 1 feeding the new switch and 1 feeding the existing one way light. This makes no impact on the outcome other than making it easier to connect up.
  7. The blue cable connects to the lighting blue cable

    View attachment 103172
To anyone reading this... Do not take the neutral from a switching line (as in the pic). In this example, what I'm trying to do is take the power from a neighbouring light switch and extend this to the light, this doesn't work and may be dangerous. The 'power' in this sense also includes a neutral to the light. This needs to come from either a lighting loop, or the consumer unit. Anything else would be for the pros only.
 
Apologies for jumping in - maybe a bit of context might help.
In older properties/ traditional wiring, you do not normally have neutral wires at light switches, all wires are live or swiched live one way or another. The neutral is taken directly to the light fitting only.

More recent installations may take neutral via the light switch position (ie looped through), because with the advent of smart switches, some require a neutral to work, so it's become more commonplace to make that provision for the future.

I suspect you may need to bring in a neutral connection - meaning from that lighting circuit - not any old neutral!

PS you say "The neutral from the light needs to go somewhere." That is the crux of the matter. I doubt you have a neutral at the switch. Just because there's a blue wire doesn't mean it's actually a neutral! If you have a test meter you can check.
yes, the blue cable is my handy work I'm afraid. I'm trying to bring the power supply and neutral to the switch, passing the neutral straight up to the light. But with my lack of knowledge, as I've seen examples in my own house where there is looping from one com to another and works for switches (perm/switching lines), I assumed that the other cable (not com) would be neutral. My error, I now know this was wrong. I therefore need to find a different supply either from a loop circuit in the attic (single storey), or take my power supply from the consumer unit. Was previously unsuccessfull in the attic. So...

Starting to get my head around getting a supply from here... obvs a B6 - old school Red/Black wiring. Any ideas how to do this?

1667215545417.png
 
Do you have any black cables in a connector block in the switch back box

An overall picture of the switch and back box may help
 
Do you have any black cables in a connector block in the switch back box

An overall picture of the switch and back box may help

This is what the 4gang looked like before the move. The 1st and 3rd from the left are in use in new 4G in position 1&2. The 2nd & 4th don't exist anymore.
FE9OSuLQ0tEHeVtIgvFLCoJQXEmeWCTo_Sw0k3oT69V4_zI7SsWxYoNr4gN0VLDRAhQENiXiGlP-PzIYJbDpjzCM77TboqLZZdBAuu6qkkvkk6ndIvdk0o9-xtNICK-ewMTuMFWYunVmWvli6ucxUd_7S8TvKFICDOf278zAnUYLjsNxUJMn3NewCojnyTM5


Just looking at the previous picture (below) from the consumer unit, i can see there is a neutral in a plastic connector is something I could use if i found its partner there too? Actually it looks like it goes to the unprotected right hand side of the rcbs
1667233669647.png
 
Last edited:
can the live and neutral come from different sources? Just looking at the picture i see there is a neutral in a plastic connector which I could share using those plastic clip connectors?
They need to come from the same circuit, by which I mean if your lighting circuit is the B6 breaker in the middle of the board (RCD protected) then the neutral needs to come from the middle of the three neutral bars (preferably terminal 4!).

There's also a B6 on the right, for a circuit which is not RCD protected, which I imagine you are not using for the lighting?

The neutral and live need to come from through the same RCD, otherwise you will have tripping problems!
 
Is there not an existing light fitting in the vicinity of where you want to put your new light, from which you could take the neutral. Or is the consumer unit nearer - it's unusual to resort to running singles from the CU!
If you do, once out of an enclosure, the cable needs to be of the sheathed type, like T&E covered in grey insulation, not just blue single insulated 🤪. I'm sure you know this.
 
Is there not an existing light fitting in the vicinity of where you want to put your new light, from which you could take the neutral. Or is the consumer unit nearer - it's unusual to resort to running singles from the CU!
If you do, once out of an enclosure, the cable needs to be of the sheathed type, like T&E covered in grey insulation, not just blue single insulated 🤪. I'm sure you know this.
the CU is just behind the partition wall - the building is brick clad timber frame, so pretty easy to work with. The CU is about 1m away, but at 90 degrees to the current wall. It's an external wall as described. Hopefully the drawing makes sense...

1667235893491.png
 
Is there not an existing light fitting in the vicinity of where you want to put your new light, from which you could take the neutral. Or is the consumer unit nearer - it's unusual to resort to running singles from the CU!
If you do, once out of an enclosure, the cable needs to be of the sheathed type, like T&E covered in grey insulation, not just blue single insulated 🤪. I'm sure you know this.

I've got this above the kitchen next to the hallway where I'm working. Looks like a bunch of live and neutrals... and what I need for my lights for both the hallway and kitchen. It looks like a lighting ring juction box with a switch cable coming from it?

Could I take my power source to my switch and neutral to the light (via the switch) as per my diagram from the spare slot on the right. And then could I also use this feed with wagos to provide L/N in the same way to my hallway switch? The switches are all in the same 4G light switch array.

Hmmm... I've just spotted that there are 2 cables coming in from the top, so there are four cables here... and there are brown and blue wires mixing. Any ideas which is which????

My guess...
  • Bottom Right Terminal = Live
  • Top Right Terminal = Earth
  • Bottom Left Terminal = Neutral
  • Top Left Terminal = Switched Live
1667310967395.png
 
Last edited:
I would hazard a guess that top left terminal is permanent live, because there's a through cable from top left to bottom, and thus the blue in the top left terminal is the L feed to the lightswitch (underneath cable at the top that returns the brown switched live to the bottom right terminal) and then the front top cable (neutral and switched live) goes to the light.

So I believe your list has top left and bottom right the wrong way round!

You need to be careful adding additional cables to those terminals, as it's easy to cross thread the grub screws when the terminal gets full, and also easy to break the head of the screw by tightening it too hard in an attempt to force too many wires in! (Not that I've ever done that🤪) However I feel, given you're doing this anyway, it is a better place to take a feed from than the CU.

You should really get a 2-pole tester to use doing this stuff, to ensure you know what is what, not 'guess'!
Eg:
 
Last edited:
I would hazard a guess that top left terminal is permanent live, because there's a through cable from top left to bottom, and thus the blue in the top left terminal is the L feed to the lightswitch (underneath cable at the top that returns the brown switched live to the bottom right terminal) and then the front top cable (neutral and switched live) goes to the light.

So I believe your list has top left and bottom right the wrong way round!

You need to be careful adding additional cables to those terminals, as it's easy to cross thread the grub screws when the terminal gets full, and also easy to break the head of the screw by tightening it too hard in an attempt to force too many wires in! (Not that I've ever done that🤪) However I feel, given you're doing this anyway, it is a better place to take a feed from than the CU.

You should really get a 2-pole tester to use doing this stuff, to ensure you know what is what, not 'guess'!
Eg:

I've got this, is this one?

1667315994659.png
 
I would hazard a guess that top left terminal is permanent live, because there's a through cable from top left to bottom, and thus the blue in the top left terminal is the L feed to the lightswitch (underneath cable at the top that returns the brown switched live to the bottom right terminal) and then the front top cable (neutral and switched live) goes to the light.

So I believe your list has top left and bottom right the wrong way round!

You need to be careful adding additional cables to those terminals, as it's easy to cross thread the grub screws when the terminal gets full, and also easy to break the head of the screw by tightening it too hard in an attempt to force too many wires in! (Not that I've ever done that🤪) However I feel, given you're doing this anyway, it is a better place to take a feed from than the CU.

You should really get a 2-pole tester to use doing this stuff, to ensure you know what is what, not 'guess'!
Eg:
I mocked up this picture as I thought it was, but if you're right where would i be connecting up to for my supply/neutral to the switch?

1667321743109.png
 
Excuse the rubbish edited version below, which is my best guess at what you have.
Using the modified labelling(!) below - I'm thinking cable 3 is the supply from the lighting circuit (eg CU or another room), and cable 4 continues the supply to the next room/ item on the circuit. (or vice versa)
You could (carefully!) check with your meter that between the SW terminal and N is 240V with the relevant light switch on, and 0V with it off (though with your high impedance meter it may show some random ghost voltage rather than 0V) and that there is 240V permanently between L and N, irrespective of any or all light switch positions.

If the above test holds true then to feed your new light with a permanent supply: L, N and E as marked up below.

If the L to N voltage goes to zero when a light switch is tuned off - see edit below


View attachment 103257
OK - so a point of clarification - does this junction box feed two lights in two different directions?
Your original scheme makes sense if your cable 2 brings power in, cable 1 goes to the switch, and cables 3 and 4 go to lights.
 
Last edited:
I mocked up this picture as I thought it was, but if you're right where would i be connecting up to for my supply/neutral to the switch?

View attachment 103247
So reassured by Loz's comment
If we've got the assumption correct, the supply terminals you need for your new light scheme are those marked N, L, and E in your diagram 👍
The cable list at the bottom of the drawing would be:
#1 light switch
#2 incoming power
#3 to light (a)
#4 to light (b)
If you can confirm the above seems where the wires go, there is a good chance your illustration is correct.
Your multimeter (carefully) connected across your labelled L & N should still show about 240V when all light switches are off!
 
Last edited:
Excuse the rubbish edited version below, which is my best guess at what you have.
Using the modified labelling(!) below - I'm thinking cable 3 is the supply from the lighting circuit (eg CU or another room), and cable 4 continues the supply to the next room/ item on the circuit. (or vice versa)
You could (carefully!) check with your meter that between the SW terminal and N is 240V with the relevant light switch on, and 0V with it off (though with your high impedance meter it may show some random ghost voltage rather than 0V) and that there is 240V permanently between L and N, irrespective of any or all light switch positions.

If the above test holds true then to feed your new light with a permanent supply: L, N and E as marked up below.

If the L to N voltage goes to zero when a light switch is tuned off - see edit below


View attachment 103257
OK - so a point of clarification - does this junction box feed two lights in two different directions?
Your original scheme makes sense if your cable 2 brings power in, cable 1 goes to the switch, and cables 3 and 4 go to lights.

FIRSTLY - MASSIVE THANKS FOR THE RESPONSES

Been upstairs and found THE junction box. It has to be the same one but the configuration is now different (🥺Uhgg!!). However, there is I think good news, this ones easier to read... I can be more sure of whats what. AND I think I have found a power supply!

However, I think I need to wire up a new junction box feeding from this one. I need two neutrals (1 Kitchen / 1 Hallway), unless I can share this in a wago in the back of the 4G switch?

1667393598615.png
 
FIRSTLY - MASSIVE THANKS FOR THE RESPONSES

Been upstairs and found THE junction box. It has to be the same one but the configuration is now different (🥺Uhgg!!). However, there is I think good news, this ones easier to read... I can be more sure of whats what. AND I think I have found a power supply!

However, I think I need to wire up a new junction box feeding from this one. I need two neutrals (1 Kitchen / 1 Hallway), unless I can share this in a wago in the back of the 4G switch?

View attachment 103291
Looks promising. Well done!
Normally the switch is in the live wire, so the light fitting is not live when you turn it off ! In which case cable 1 ought to be the switch and cable 2 the light - does that make sense?
It seems cable 3 is the permanent supply you need. You mention cable 3 comes from a Wago joint - could you put a Wago box or junction box there to take a feed from, or alternatively take a T&E to feed your new circuit out of the box you show here.

Note the long stripped bare copper on the black hanging out of the SW terminal - looks like it's falling out. I would try re-making that terminal (power off of course!) The idea is not to have any bare copper on display, so insulation should run up close to the terminals, and the E wires should have sleeving. Similarly cable 3 has some single insulated cable outside the junction box, which is poor practice. Appreciate this is not your fault, and you may know all this, but I just thought it worth pointing out if not!

You could normally accommodate a Wago for N's in the back of a deepish box, but with your 4 gang switch it might be tight? Can you not distribute the neutral to the lights above the ceiling (as per your very first diagram) - why take it to the switch box?
 
Last edited:
Looks promising. Well done!
Normally the switch is in the live wire, so the light fitting is not live when you turn it off ! In which case cable 1 ought to be the switch and cable 2 the light - does that make sense?
It seems cable 3 is the permanent supply you need. You mention cable 3 comes from a Wago joint - could you put a Wago box or junction box there to take a feed from, or alternatively take a T&E to feed your new circuit out of the box you show here.

Note the long stripped bare copper on the black hanging out of the SW terminal - looks like it's falling out. I would try re-making that terminal (power off of course!) The idea is not to have any bare copper on display, so insulation should run up close to the terminals, and the E wires should have sleeving. Similarly cable 3 has some single insulated cable outside the junction box, which is poor practice. Appreciate this is not your fault, and you may know all this, but I just thought it worth pointing out if not!

You could normally accommodate a Wago for N's in the back of a deepish box, but with your 4 gang switch it might be tight? Can you not distribute the neutral to the lights above the ceiling (as per your very first diagram) - why take it to the switch box?

Well I now have kitchen lights, but a weird thing happened. I turned off all the lights and 16amp breakers too at the CU, and after connecting to the wago upstairs and feeding it back to the 4G downstairs I was trimming off the end for connecting and it cut off all the power, so it must have been 'live'.

But the strange thing is i know that the single light in the kitchen goes off when turn the light 6/16's off. Going to test it again now... the single spot went off. I tried the lights (kitchen pendants) and they were off. Going to try with the multireader. Getting power with the power on and not when off. Hmmmm maybe I didn't turn off all of the 6&16s at the CU, but I'm pretty sure I turned at least the one I needed to off.

Anything like that ever happen to you?

Going to tidy up and connect the hallway lights using a wago at the switch for the hallway lights too. BTW its a partition wall and there's plenty of room back their after nibbling at the insultation we used.

Another thing just occuring to me is that the L/N I've gone into is brown/blue. The cables at the CU are all red/black. However I still think we made the right call at JB. I guess its coming off another JB, and possibly a 32amp ring circuit 🤪 (not my work)

1667402767170.png
 
Last edited:
Looks promising. Well done!
Normally the switch is in the live wire, so the light fitting is not live when you turn it off ! In which case cable 1 ought to be the switch and cable 2 the light - does that make sense?
It seems cable 3 is the permanent supply you need. You mention cable 3 comes from a Wago joint - could you put a Wago box or junction box there to take a feed from, or alternatively take a T&E to feed your new circuit out of the box you show here.

Note the long stripped bare copper on the black hanging out of the SW terminal - looks like it's falling out. I would try re-making that terminal (power off of course!) The idea is not to have any bare copper on display, so insulation should run up close to the terminals, and the E wires should have sleeving. Similarly cable 3 has some single insulated cable outside the junction box, which is poor practice. Appreciate this is not your fault, and you may know all this, but I just thought it worth pointing out if not!

You could normally accommodate a Wago for N's in the back of a deepish box, but with your 4 gang switch it might be tight? Can you not distribute the neutral to the lights above the ceiling (as per your very first diagram) - why take it to the switch box?

So I have the live and neutral to the quick fit connectors keeping it to a single cable to the terminal in the switch. How would I go about connecting the live and neutral to the hallway lights using the single cable i have running to the 4G switch. Does it matter if they share the same 'connector' fitting. To be clear this is the type I'm using...
1667404850646.png
 
I was trimming off the end for connecting and it cut off all the power, so it must have been 'live'.
If you inadvertently shorted neutral to earth that can trip the RCD, even with that circuit's MCB off,
That is 'normal behaviour' 🙂
 
So reassured by Loz's comment
If we've got the assumption correct, the supply terminals you need for your new light scheme are those marked N, L, and E in your diagram 👍
The cable list at the bottom of the drawing would be:
#1 light switch
#2 incoming power
#3 to light (a)
#4 to light (b)
If you can confirm the above seems where the wires go, there is a good chance your illustration is correct.
Your multimeter (carefully) connected across your labelled L & N should still show about 240V when all light switches are off!

Urgg not so fast... there's a gremlin in the connection somewhere.

The test of the light switches saw it fail. And it was the 32amp fuse that tripped everytime. I checked the JB for that loose cable and found that the earth was loose from the switch/light cable. I refitted the one you spotted at the bottom terminal, although wasn't clear if it was loose. However the fact that the 32amp fuse tripped I'm going to change the single spot in the ktichen too when I find a lighting loop, or I might just bite the bullet and go for the CU.

So I either need to find another
 
So I have the live and neutral to the quick fit connectors keeping it to a single cable to the terminal in the switch. How would I go about connecting the live and neutral to the hallway lights using the single cable i have running to the 4G switch. Does it matter if they share the same 'connector' fitting. To be clear this is the type I'm using...
View attachment 103294
Sorry I'm not quite understanding the issue.
Yes you can put another L cable into the unoccupied slot of the non-wago Wago!
Similarly for a neutral into a further Wago, and earth etc.
But they will ultimately have to be put in an enclosure, which also encloses all single insulated bits of cable.
(Search "Wago box")
eg WAGOBOX Junction Box 108 x 39 x 44 mm | Toolstation - https://www.toolstation.com/wagobox-junction-box/p92231
 
Sorry I'm not quite understanding the issue.
Yes you can put another L cable into the unoccupied slot of the non-wago Wago!
Similarly for a neutral into a further Wago, and earth etc.
But they will ultimately have to be put in an enclosure, which also encloses all single insulated bits of cable.
(Search "Wago box")
eg WAGOBOX Junction Box 108 x 39 x 44 mm | Toolstation - https://www.toolstation.com/wagobox-junction-box/p92231

I'm not sure whats causing the issue but I'm getting weird behaviour, it may be overloading. The lights stopped working altogether after switching on the kitchen lights and then the outdoor lights (all in the same 4g switch). The 32amp tripped when turning the power back on, but stayed up once i tried the switch again.

I take your point about working tidy as it were, while I'm in 'seeing what works' mode I'm taking shortcuts, cables pinned in place, sheeths etc. Once I know I've got the solution there will be a 'completion' phase.

Back to the issue at hand...

Q: Does the mere fact its a 32amp circuit I've linked into have the type of impact I'm seeing, and if not then is it simply a question of re-wiring the JB to include my new L/N to the switch. Does it mean that I already have an issue on that circuit which I'm simply exaserbating with the additional wiring. I'm using 1.5mm cable for the L/N to the switch.
 
I'm not sure whats causing the issue but I'm getting weird behaviour, it may be overloading. The lights stopped working altogether after switching on the kitchen lights and then the outdoor lights (all in the same 4g switch). The 32amp tripped when turning the power back on, but stayed up once i tried the switch again.

I take your point about working tidy as it were, while I'm in 'seeing what works' mode I'm taking shortcuts, cables pinned in place, sheeths etc. Once I know I've got the solution there will be a 'completion' phase.

Back to the issue at hand...

Q: Does the mere fact its a 32amp circuit I've linked into have the type of impact I'm seeing, and if not then is it simply a question of re-wiring the JB to include my new L/N to the switch. Does it mean that I already have an issue on that circuit which I'm simply exaserbating with the additional wiring. I'm using 1.5mm cable for the L/N to the switch.
You really should not be connecting lights to a 32A circuit. Apart from not to regs and not safe, the 32A breaker is too big to protect 1.5, even 2,5mm cable. Also if you end up mixing your 32A L with a neutral from a 6A lighting circuit on the other half of the CU, you will be tripping the RCD.
I didn't realise you were pursuing using that 32A circuit. Please don't.
You need to use power from the RCD protected 6A MCB circuit, and only that circuit. Sorry, but that is absolutely essential.
 
I hate to sound negative but I think it's time to accept your are out of depth and need an electrician in for this work. There's no shame in knowing your limits
 
You really should not be connecting lights to a 32A circuit. Apart from not to regs and not safe, the 32A breaker is too big to protect 1.5, even 2,5mm cable. Also if you end up mixing your 32A L with a neutral from a 6A lighting circuit on the other half of the CU, you will be tripping the RCD.
I didn't realise you were pursuing using that 32A circuit. Please don't.
You need to use power from the RCD protected 6A MCB circuit, and only that circuit. Sorry, but that is absolutely essential.

Yes we're thinking alike...

Need to seperate out the facts I think:
  • The electrics tripped when I cut the cable I was taking to the switch from the cable that feeds the JB. The 6 & 16s were all off at the CU.
  • There was strange behaviour when I turned on other lights in the same switch (not connected), which then didn't work at all.
  • The spot light and switch which are fed from the JB turn on and off with the 6amp fuse in the CU switched on/off.
  • The lights worked when I connected them up to the wiring config I'm using from GSH Electrics (teacher/practitioner), seemed brighter.
So, unless someone's got some tests I can do to narrow down what the actual issue may be, given all of the above I guess I need to find another source for my supply and also take the single spot off that 32 end loop.

Tests I imagine would be measuring the voltage or amps at each connection in the attic. There are enough cables up there, and we do have lighting in this corner of the bungalow.

I don't thinks its a question anymore of re-wiring that JB.
 
I hate to sound negative but I think it's time to accept your are out of depth and need an electrician in for this work. There's no shame in knowing your limits
I take your point, and agree. Also, I know assumptions are dangerous, I work in Testing software. I thought that as this was feeding spot lights previously and now just the one, that this would be a good one to use. I should have checked it for 'live' after the RCBs were turned off.

But anyway, I take your point and I'm very close to solving this. I'm learning a lot in the process. I wear 'marigolds' :).
 
  • Funny
Reactions: DPG
Yes we're thinking alike...

Need to seperate out the facts I think:
  • The electrics tripped when I cut the cable I was taking to the switch from the cable that feeds the JB. The 6 & 16s were all off at the CU.
  • There was strange behaviour when I turned on other lights in the same switch (not connected), which then didn't work at all.
  • The spot light and switch which are fed from the JB turn on and off with the 6amp fuse in the CU switched on/off.
  • The lights worked when I connected them up to the wiring config I'm using from GSH Electrics (teacher/practitioner), seemed brighter.
So, unless someone's got some tests I can do to narrow down what the actual issue may be, given all of the above I guess I need to find another source for my supply and also take the single spot off that 32 end loop.

Tests I imagine would be measuring the voltage or amps at each connection in the attic. There are enough cables up there, and we do have lighting in this corner of the bungalow.

I don't thinks its a question anymore of re-wiring that JB.
Here's the layout again of the bungalow.

As you can see the CU is very close to the 4G switch. It will be a more messy job, but once all the powers off in the CU I know I'm connecting to either 16 or 6, probably 6. I would double up in the top with the live wire, and then would I have to connect to the same neutral and earth bars 'number' as the existing cable in the RCB or just ensure I use the same for the new wires? I know that I would have to use the same bar that corresponds to the same section of RCBs.

Diagram below: The faded cream area in the middle represents the boradrd crawl way in the attic. It's spider man after that to get to the lights and down holes for the cables I've used so far. There are spots on that side of the house too, there's a pendant in the master bedroom but thats a long way from where I'm working. Closest are the spots, I guess if I were to go there looking for my L/N then there would have to be something feeding these spots. But thats all under boards... and difficult to get to. I'm liking the CU more now as an option. BUT it would be good to understand exactly what was going on with the JB.

1667483348415.png
 
You really should not be connecting lights to a 32A circuit. Apart from not to regs and not safe, the 32A breaker is too big to protect 1.5, even 2,5mm cable. Also if you end up mixing your 32A L with a neutral from a 6A lighting circuit on the other half of the CU, you will be tripping the RCD.
I didn't realise you were pursuing using that 32A circuit. Please don't.
You need to use power from the RCD protected 6A MCB circuit, and only that circuit. Sorry, but that is absolutely essential.

I've got what looks like 2.5 and 1.5mm cables running around the edge of the attic. Would it be safe to assume before I cut into the lower one is lighting loop and the top one is for a mains loop? Bungalow was built in the eighties...

1667488153857.png


And then I have this set up, not my work, close by... the white round thing looks like a junction box. And the white cable goes off to what I think is the conservatory lights.

1667488844045.png
 
I've got what looks like 2.5 and 1.5mm cables running around the edge of the attic. Would it be safe to assume before I cut into the lower one is lighting loop and the top one is for a mains loop?
Don't cut into anything before understanding EXACTLY what it is. Preferably don't cut into anything full stop!
Please deal with this in an analytical manner, which you should be capable of if testing s/w professionally.

You need to understand what cable does what and goes where in your existing wiring, map out what needs to be done, and test the validity of your assumptions (eg using a meter) before actually connecting anything.
Don't just try things out to see if they work. Electrics should be done with test equipment and logic.

I'm leaving this, hoping you either get someone in to help/do it, or you spend a lot more time reading up, investigating, testing, using logic and gaining certainty about your existing wiring before trying to connect anything up.
 
I have been following this thread on and off and whilst the forum is happy to help with DIY questions this is getting well beyond what is acceptable and we must consider your safety being a non-electrical person. @Avo Mk8 has given much advice but now quite rightly has drawn a line under it, you need professional help.
 
Don't cut into anything before understanding EXACTLY what it is. Preferably don't cut into anything full stop!
Please deal with this in an analytical manner, which you should be capable of if testing s/w professionally.

You need to understand what cable does what and goes where in your existing wiring, map out what needs to be done, and test the validity of your assumptions (eg using a meter) before actually connecting anything.
Don't just try things out to see if they work. Electrics should be done with test equipment and logic.

I'm leaving this, hoping you either get someone in to help/do it, or you spend a lot more time reading up, investigating, testing, using logic and gaining certainty about your existing wiring before trying to connect anything up.
thanks for your help, amazed you hung on so long actually :) Really appreciated it.
 
If you inadvertently shorted neutral to earth that can trip the RCD, even with that circuit's MCB off,
That is 'normal behaviour' 🙂
It can't be a 32amp supply. The light over the sink goes off when I turn off the 6amp RCB (see pics below). So it must be a 6amp junction box. Which means that there is something else causing the intermittent behaviour I experienced when trying the kitchen lights. This can only be wiring related, either at the junction box or the light switch.

Picture #1 = 6 amp fuse in OFF position
Picture #1 = Light switch in ON position
Picture #3 = Single spot not ON

I'm going to test tomorrow at the junction box pictured below using my multireader, with the power on/off at this 6 amp fuse. I'll test against E/L N/L. I guess theres another test with the 32amp on/off too just to completely discount it.

If testing is positive for 6amp I'lll move on to the wiring at the junction box, then if still experiencing issues will rewire the 3 way lighting as to a different format AC Power showed me on DIY Forums.

If this doesn't solve it then either get the pro's in or go at the CU.

Seems like a logical approach... let me know if you think otherwise.

1667581072734.png

1667581143528.png
 
Status
Not open for further replies.

Reply to Lights - Why is the my supply switch controlling my new one? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
575
Hi I want to add a light to my attic. There is a single switch on the landing that I want to change to a double switch and then use it to still...
Replies
24
Views
2K
I have a strip light in the kitchen operated from a single switch. I want to replace it with a straight bar 4 spot array. There are three supply...
Replies
2
Views
487
Hi everyone, after temporary removing a Sonoff that I've installed years ago to do some painting, I'm unable to get everything back to work. I've...
Replies
4
Views
525
Hi everyone, I really hope someone will be able to help. So last night I tried to change 2 ceiling rose / pendant lights at my mother in laws...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock