has anyone done this,

got a customer who wants a t8 batten in one with a sandblasted glass cover, will be double boarded inside it then fitting and wiring on to then blasted cover to conceal, but will it need venting for heat etc, any opinions gratefull, can show drawings too
 
The calculations could be done to prove it for certain, but I would think an RSJ of that size would act as a huge heatsink so wouldn't be an issue.

You have the fire protection for the RSJ covered with double boarding, but you can single board it if you use fireboard instead. That'd give you a little more depth to work with. BC here only require single thickness boarding on RSJ's now as that gives half hour protection, but as fireboard is only maginally dearer it's belt and braces and customers often appreciate the thought.
 
Why are you boarding the JSJ web? What is the board going to protect? It's a light fitting not a oxy-propane cutting torch!
The web will be 15mm thick solid steel!
 
Because the building regs require it.

Part B Volume 1 4.2
"Elements of structure such as structural frames, beams, columns, load bearing walls (internal and external) floor structures and gallery structures should have at least the fire resistance given in Appendix A, Table A1." This relates to the tests in BS476-21.

If you cut through all the "blah, blah" there needs to be sufficient fire protection to prevent a steel support (RSJ) reaching 550 deg c within half an hour. There are a number of way to do this, sprays, coatings etc etc. |The cheapest and easiest is to 'wrap' the beam in 12.5mm plasterboard which is deemed to have fire break through resistance of 30 minutes.
 

Reply to ligthing in rsj cavity in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top