Line to Earth fault 70 volts?!?

Discuss Line to Earth fault 70 volts?!? in the UK Electrical Forum area at ElectriciansForums.net

I

iamgary25

Just tested a lighting circuit to find that the voltage between Line and Neutral was 240V and Line to Earth was around 70 volts? What could this be? a short between Line and Earth? Also the circuit is on a 6A 30mA RCBO but doesn't trip, the test button works though...

thanks
 
Line to Earth was around 70 volts? What could this be? a short between Line and Earth

Does not compute... you can't have a voltage across a short!
 
Test kit out ,if you have 70 volts between line and earth your earth is possibly open circuit , and if all was ok and you had a line to earth fault i would expect a Bang !!! so you need to carry out an r1r2 test ,ir test etc
 
Just tested a lighting circuit to find that the voltage between Line and Neutral was 240V and Line to Earth was around 70 volts? What could this be? a short between Line and Earth?
A problem possibly but 70V is hardly indicative of a short circuit.
Maybe the neutral not connected to earth so the system is floating?
Have you checked that?
 

Reply to Line to Earth fault 70 volts?!? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock