Discuss Live cable taken straight off busbar..Reg no. required. in the UK Electrical Forum area at ElectriciansForums.net
How about the cover missing off the busbars? Note the screw holes.I cant think of any regulation that prevents lugging a cable to a pre-drilled bolt on a busbar.
Evening...Can anyone tell me which reg this breaks??
It feeds a switched fuse.
View attachment 39039
I didn't have my pinhole camera with me that day to take a picture with the cover on, so had to take the cover off for the picture! It was only off for seconds..promise.How about the cover missing off the busbars? Note the screw holes.
So, has the cover been adapted/altered to accommodate the extra cable? I wouldn't have thought it was manufactured to.I didn't have my pinhole camera with me that day to take a picture with the cover on, so had to take the cover off for the picture! It was only off for seconds..promise.
See#12.....and the fixing holesI'm not sure these boards even had a cover over those bars, they are on the load side of the isolator and a lot of boards of that vintage didn't cover the bars on the load side. I'd agree with checking carefully for any thermal or mechanical damage caused by the termination....but otherwise, don't think I'd be overly concerned if I came across it on an EICR.
No that board never had busbar covers and how anyone can look for excuses to find that acceptable is beyond me.
There is a cover for the busbars, it was just loosely placed over as the offending cable prevents it being screwed down. I would have to notch out the cover to fix it down.Is it over 3 meters? Lol
I agree but I would not like to make a judgement on a non recommended ad hoc connection that it does not pose a danger as you have nothing to gauge it against. It is difficult to see but the only way that lug can be fitting flat to the busbar is if it has broken the plastic busbar support which it looks like it has.There's a difference between finding something acceptable to do and finding an existing bodge dangerous enough to recommend immediate disconnection.
That’s ok then.Drill a hole elsewhere on the busbar !!
But yes that is a busbar support with the bolt captive in the bakelite so you could never tighten it too much.
No that board never had busbar covers QUOTE]
Mystic Meg?
Hopefully there isn't an MCB with more than one cable connected as well or you'll have the place evacuatedI will Code it no matter where it is.
You could gauge it by the fact that it has almost certainly been there for a considerable time, (red cable), and seems not to have spontaneously combusted yet.I agree but I would not like to make a judgement on a non recommended ad hoc connection that it does not pose a danger as you have nothing to gauge it against. It is difficult to see but the only way that lug can be fitting flat to the busbar is if it has broken the plastic busbar support which it looks like it has.
If this was a domestic board and the connection was on the busbar you would all code it on an EICR .
Oops - missed thatIf you expand the photo, you can see that the nut and bolt is connecting two lengths of busbar.
I would call in something else.I wouldn't do it but can we just call it unorthadox?
I wonder if he would call this the same?I would call in something else.
Would you care to quote the regulation you are basing that on?
Reply to Live cable taken straight off busbar..Reg no. required. in the UK Electrical Forum area at ElectriciansForums.net