Discuss Live metal casing on new light in the Lighting Forum area at ElectriciansForums.net

Bigalz

DIY
Reaction score
0
Hi guys looking for advice here,

Voltage on light casing!

Just been out and bought a new light fitting (I will attach the photo of said light) simple 2 core and earth terminal connections.
After install i wanted to check the lower ring of the light to see if it had earth continuity from the suspended ring that has 3 metal bosses, and noticed it was very high at 18.3Mohms
Checked for voltage between metal boss and metal ceiling rose and I’m getting 45v ??

Any idea why I’m gettting this ? I’ve already returned one and this is the second one from Costco and still same problem.

Cheers.
 
TL;DR
Voltage on metal casing

Attachments

  • image.jpg
    535.8 KB · Views: 30
The lower section may not actually be solidly connected to earth by intention. The wires from the top section to the lower ring may be insulated/routes.on such a way that it is not necessary, and maybe only the main body of the light is earthed.

Hard to believe that each of the 3 arms has defective earth continuity as a result of poor manufacture.
 
Last edited:
Hi guys looking for advice here,

Voltage on light casing!

Just been out and bought a new light fitting (I will attach the photo of said light) simple 2 core and earth terminal connections.
After install i wanted to check the lower ring of the light to see if it had earth continuity from the suspended ring that has 3 metal bosses, and noticed it was very high at 18.3Mohms
Checked for voltage between metal boss and metal ceiling rose and I’m getting 45v ??

Any idea why I’m gettting this ? I’ve already returned one and this is the second one from Costco and still same problem.

Cheers.
Dodgy fitting design Mate I recon, try a different supplier
 
The lower section may not actually be solidly connected to earth by intention. The wires from the top section to the lower ring may be insulated/routes.on such a way that it is not necessary, and maybe only the main body of the light is earthed.

Hard to believe that each of the 3 arms has defective earth continuity as a result of poor manufacture.


Agreed, but the main issue being the voltage between the 3 boss’ to metallic ceiling rose ?
 
I can’t see any wires from the boss to the ring, are the rods being used to pass electricity at a low voltage to it?
 
Voltage on light casing!
Just had a look and your light (in fact other styles from this manufacturer also) has a bona fide safety approval from an accredited CSA test house. I would feel confident that it has been designed and manufactured to be safe.

As said the lower part is likely to be isolated from the ceiling fitting containing the driver.
This is not a technical explanaton, but I would say it's not unusual to see an 'induced'/ capacitively coupled voltage on isolated parts when measured with a high impedance instrument. Once you introduce a 'load', eg by touching it (!), the minute current from the high impedance source (so no shock) results in the voltage disappearing to almost zero.

This is an artefact of using a high impedance meter. You often see threads on this forum where someone's found a strange voltage on an isolated cable and believe's it's a fault - but it's not always ?

Are you in UK or Canada? oK - sorry didn't see the location! - thanks Tel ?
 
Last edited:
I don't think there is a "Fife" in Canada. 50 characters again. come on Dan,
 

Reply to Live metal casing on new light in the Lighting Forum area at ElectriciansForums.net

Similar Threads

DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
442
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
636
Metal building with living quarters the panel is on the outside and about 20 feet away from new build that will be 2x6 what type of shielded wire...
Replies
3
Views
557
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
534
Recently bought a none contact voltage tester and decided to use it on a few things around the house but a metal bedroom light is lighting up red...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock